Encoders best CPR
12 years 6 months ago #46421 by greeder88
Encoders best CPR was created by greeder88
What is the recommended CPR for milling machine encoders? I assume too high a count slows the rapid speed? Too low makes oval circles?
12 years 6 months ago #46423 by emcPT
Replied by emcPT on topic Encoders best CPR
I recommend that you make your calculations so that you could achieve a theoretic resolution of 0.0001mm or less (I use this to obtain 0.001 real position, where your drive could work out with 10 encoder positions to make its internal calculations and therefor achieve the 0.001).
You need to make your calculations based on the screw pitch and reduction to get the encoder resolution.
It can lower your step rate depending on the hardware that you choose.
The following user(s) said Thank You: greeder88
12 years 6 months ago #46431 by greeder88
Replied by greeder88 on topic Encoders best CPR
I an getting some weirdness with the scale factor.
I put three different encoders on my machine and scaled so I have .100 inch of travel per motor revolution which is what I require.
Encoder 1 has 250ppr and needs a scale factor of 10,000
Encoder 2 has 1000ppr and needs 40,000
Encoder 3 has 1024ppr and needs 20,480
Encoder 3 is only getting half the counts it should.
They are all the same BEI ABZC indexed encoders.
I can live with the lower count but does anyone know what happened?
Also a spare encoder is open collector not line driver. Is there a way to use it with a converter chip of some sort or should I get rid of it?
12 years 6 months ago #46432 by PCW
Replied by PCW on topic Encoders best CPR
I would check encoder 3's output signals (sounds like an encoder or wiring fault)
Its possible to use open collector encoders but you may need pullup resistors
to 5V on the A/B/Z wires (most mesa encoder inputs have these pullups)
12 years 6 months ago - 12 years 6 months ago #46433 by jmelson
Replied by jmelson on topic Encoders best CPR
greeder88 wrote: What is the recommended CPR for milling machine encoders? I assume too high a count slows the rapid speed? Too low makes oval circles?
It depends somewhat on the technology of the servo system.
I have 20,000 counts/inch on X and Y and 40,000 counts/inch on Z on my
Bridgeport mill, with analog velocity servos. This works well.
However, on my minimill with PWM servos I have 128,000 counts/inch,
and wouldn't mind having more.
The only time encoder resolution is likely to be a speed limit is
with software generated step pulses and step-servos like the
Gecko G320 drives.
Too low resolution won't make oval circles, it will make stairsteps
on certain moves where one axis is moving slowly while the other
one moves fast.
As for open collector encoders, just use a resistor to pull all
outputs up to +5 V. Generally, 1 K Ohm resistors should work
fine.
Jon
Last edit: 12 years 6 months ago by jmelson.
12 years 6 months ago - 12 years 6 months ago #46463 by greeder88
I learned that if you get your encoder B,B_ sequence reversed you loose half your counts unless you also reversed the A,A_ then your good.
Also learned you should hook up the 0v first (While you mind is less confused). I found out the 0v wire is the killer of encoders if you get that wrong.
I changed the jumpers on the 7i77 to single ended and my open collector encoder worked!
With the jumpers switched would I still have a Differential encoder since the encoder has the A, A-.B,B-,Z,Z- ? Or does the jumper take the (not ones) out of action?
Last edit: 12 years 6 months ago by greeder88. Reason: Made it clearer
Moderators: PCW, jmelson
Time to create page: 0.192 seconds