Spindle orient PID tuning [re-solved, yay]
14 May 2022 23:49 #242989
At this point it might well be worth trying the inverse deadband.
Actually I would probably use a lincurve to give the same effect.
Or, possibly first, I would set up a variable gain (again using lincurve).
If the error is within the orient complete window, then the P-gain would be low.
At each side of that, the P-gain would be set up so that the output is at least 60 rpm. (eg, at 2 degrees on the X the Y would be 30, for a PID output of 60 degrees, 20 at 3, 15 at 4 etc.
Having typed all that, I have looked at the other post and see that your P gain is 2000. Is the feedback to the PID in degrees or in revs?
Replied by andypugh on topic [So close...] Spindle orient PID tuning?
This sounds like it is sitting in a position such that the P-term isn't big enough to request 60rpm. Then eventually the I-term integrates enough to get to 60rpm, but then it takes too long for the I to integrate down again. (This is a phenomenon called "I term wind-up"Seems like once in a while it'll get close (within a couple degrees), stop, then jump and hunt until orient times out and errors.
- spumco
- Thank you received: 905
15 May 2022 01:35 #242995
by spumco
Replied by spumco on topic [So close...] Spindle orient PID tuning?
I think it's in revs:
setp [HMOT](CARD0).encoder.00.counter-mode 0
setp [HMOT](CARD0).encoder.00.filter 1
setp [HMOT](CARD0).encoder.00.index-invert 0
setp [HMOT](CARD0).encoder.00.index-mask 0
setp [HMOT](CARD0).encoder.00.index-mask-invert 0
setp [HMOT](CARD0).encoder.00.scale [SPINDLE_0]ENCODER_SCALE
net spindle-revs <= [HMOT](CARD0).encoder.00.position
net spindle-vel-fb-rps <= [HMOT](CARD0).encoder.00.velocity
net spindle-vel-fb-rpm <= [HMOT](CARD0).encoder.00.velocity-rpm
net spindle-index-enable <=> [HMOT](CARD0).encoder.00.index-enable
I looked at the inverse-deadband thing you mentioned and that's a non-standard component, right? I'd have to install it (somehow) before using it - not sure how to do that.
Same thing for lincurve. I read up on the comp - looks useful - and I get how to create the x/y lookup chart, but I'm hazy on how to connect that chart a PID P-gain function. Forum searching reveals some useful lincurve examples for an anolog spindle speed correction, but I've not found anything for other applications.
-Ralph
-Ralph
17 May 2022 00:04 #243117
(This is, unfortunately, a little bit circular, you either have to accept a stale error into the lincurve or have the PID gain change a cycle too late, depending on whether the "addf" of the Lincurve is before or after the "addf" for the pid.)
You would connect the pid.N.error output to the X of the lincurve, then take the Y out of the lincurve to control the P-gain of the PID.Same thing for lincurve. I read up on the comp - looks useful - and I get how to create the x/y lookup chart, but I'm hazy on how to connect that chart a PID P-gain function.
- spumco
21 May 2022 03:07 #243456
by spumco
(I'm back to fiddling with orient while I'm waiting on a reply to the carousel thing)
Here's what I've got in the test HAL:
#setp pid.o.Pgain 2000 #[TUNE]P
setp pid.o.Igain 0 #[TUNE]I
setp pid.o.Dgain 250 #[TUNE]D
setp pid.o.bias 0 #[TUNE]BIAS
setp pid.o.FF0 0 #[TUNE]FF0
setp pid.o.FF1 0 #[TUNE]FF1
setp pid.o.FF2 0 #[TUNE]FF2
setp pid.o.deadband 0.005 #[TUNE]DEADBAND
setp pid.o.maxoutput 210 #[TUNE]MAX_OUTPUT
setp pid.o.error-previous-target true
setp orient.0.tolerance 0.8
setp lincurve.0.x-val-00 0
setp lincurve.0.y-val-00 0
setp lincurve.0.x-val-01 0
setp lincurve.0.y-val-01 0
setp lincurve.0.x-val-02 0
setp lincurve.0.y-val-02 0
setp lincurve.0.x-val-03 0
setp lincurve.0.y-val-03 0
setp lincurve.0.x-val-04 0
setp lincurve.0.y-val-04 0
net orient-lincurve-in <= pid.o.error
net orient-lincurve-in => lincurve.0.in
net orient-lincurve-out <= lincurve.0.out
net orient-lincurve-out => pid.o.Pgain
Obiously I've set the lincurve pairs to 0 as this was a cut-paste from a thread on spindle pwm control.
Suggested starting pair values based on the earlier 'moderately close' orient behavior with P=2000?
Your patience is remarkable, BTW.
21 May 2022 16:33 #243484
Something like
-5, 2000
-2, 10000
-1, 0
1, 0
2, 10000
5, 2000
To start with.
-5, 2000
-2, 10000
-1, 0
1, 0
2, 10000
5, 2000
To start with.
- spumco
22 May 2022 03:11 #243529
by spumco
So lincurve addition didn't throw any errors and I started running/tuning orient.
M19 kept timing out... and I noticed something strange in halshow.
orient.0.poserr always winds up way off - which, presumably, is why it times out with an error. But poserr looks funny, like a scaling issue or something. The spindle is getting close and the PID is twitching/hunting, but poserr is reporting almost a full turn off.
What would cause the orient poserr to be almost a full turn off, yet the PID thinks the target is close enough to be wagging +/- just a little?
22 May 2022 10:29 #243546
I think that there is a scaling issue, indeed. It's in the lincurve. The example I gave you was in degrees, but the pid loop is working in turns.
Divide all the X by 360, and also make the centre deadband smaller, as you have a 0.5 degree tolerance. ie make the +1 and -1 +0.2/360 and -0.2/360 so that the PID only goes quiet when the spindle is inside the window.
- spumco
11 Jun 2022 15:06 #244939
by spumco
Replied by spumco on topic [At the Finish Line] Spindle orient PID tuning?
Thank you Andy - the scaling put me on the right track.
Adjusted the lincurve & deadband and it's no longer wagging dramatically. Still twitching a bit, but with the earlier lincurve values divided by 360, deadband = 0.003, and tolerance = 0.2 it's achieving 'is-oriented' within a second or two.
I copied the basic scheme from this thread:
forum.linuxcnc.org/10-advanced-configura...le-lock-brake#225912
with the thought that having an electronic spindle/orient 'brake' would be useful.
It's decision time - do I abandon the 'brake' function, or do I try to tune the remaining wiggle out down to a few counts?
Any suggestions on getting more of the wiggle out?
- spumco
11 Jun 2022 22:31 #244962
by spumco
Replied by spumco on topic Spindle orient PID tuning? [So close but no dice]
While not back to square 1, orient is starting to aggravate me.
It's not repeatable. I can run an M19 orient command four times in a row, and it doesn't respond the same way twice. I set up a halscope to see if that helped make sense of what's happening.. but it isn't helping me understand the seemingly random responses.
I've got a simple little program to run the spindle for a couple seconds, stop it, then orient. I'm giving it 3 seconds to orient before it throws an error.
Multiple tests with the same lincurve & deadband values result in wildly different results. It usually orients the first or second time if I tweak an input value, but after that it's hopeless. Or it will fail four times in a row... then it nails the orient in less than a second.
Adding a little (relatively) I-term seems to have helped, but it's not what I'd call reliable.
Multiple screen captures attached - all are with the same settings. First one nailed it, remainder failed.
- Thank you received: 5330
12 Jun 2022 02:06 #244969
Replied by PCW on topic Spindle orient PID tuning? [So close but no dice]
My take on this is discard lincurve and fix the orient component so it outputs
a followable motion command (add orient velocity and acceleration constraints)
That way the PID heavy lifting will be done by FF1 like a standard velocity mode
servo. Step command inputs and integral terms don't get along very well
Time to create page: 0.389 seconds