2.2kw VFD Spindle wiring to Mesa 7i76e
- jackdavies
-
Topic Author
- Offline
- Junior Member
-
Less
More
- Posts: 21
- Thank you received: 4
15 Oct 2018 21:53 #118851
by jackdavies
2.2kw VFD Spindle wiring to Mesa 7i76e was created by jackdavies
The following user(s) said Thank You: deanforbes
Please Log in or Create an account to join the conversation.
- Hakan
- Offline
- Platinum Member
-
Less
More
- Posts: 1317
- Thank you received: 453
15 Oct 2018 22:54 #118855
by Hakan
Replied by Hakan on topic 2.2kw VFD Spindle wiring to Mesa 7i76e
I have not connected the Huan Yang vfd to the 7i76e. Instead I used USB-RS485 converter like this one
www.ebay.com/itm/CH340-USB-to-RS485-485-...Sw7XZXhzJe:rk:2:pf:0
together with the hy_vfd module
www.ebay.com/itm/CH340-USB-to-RS485-485-...Sw7XZXhzJe:rk:2:pf:0
together with the hy_vfd module
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 19888
- Thank you received: 4646
18 Oct 2018 19:12 #119013
by andypugh
Replied by andypugh on topic 2.2kw VFD Spindle wiring to Mesa 7i76e
+10 to Pin 3
VI to pin 2
ACM to Pin 1
FOR to Pin 6
REV to Pin 8
DCM to Pins 7 and 5
Then Configure the VFD
PD001 = 1
PD002 = 1
PD044 = 1
PD045 = 5
VI to pin 2
ACM to Pin 1
FOR to Pin 6
REV to Pin 8
DCM to Pins 7 and 5
Then Configure the VFD
PD001 = 1
PD002 = 1
PD044 = 1
PD045 = 5
The following user(s) said Thank You: TheChosenOne, deanforbes, Sadmeatball, benqick
Please Log in or Create an account to join the conversation.
- Marki123
- Offline
- Senior Member
-
Less
More
- Posts: 48
- Thank you received: 1
28 Feb 2021 13:53 #200418
by Marki123
Replied by Marki123 on topic 2.2kw VFD Spindle wiring to Mesa 7i76e
Hi, i have a HY02D223B Ver.2 i think. Did anyone have an idea how to connect them right to the 7i76e? Or would it be better to only work with the RS485 Modbus
Please Log in or Create an account to join the conversation.
- kkuehn
-
- Offline
- New Member
-
Less
More
- Posts: 15
- Thank you received: 2
28 Feb 2021 20:01 - 28 Feb 2021 20:03 #200460
by kkuehn
Replied by kkuehn on topic 2.2kw VFD Spindle wiring to Mesa 7i76e
Modbus is preferable in my opinion because it allows you to have information from the VFD available in LinuxCNC. I currently have a pyvcp panel set up to display the current draw from the VFD and the approximate spindle speed based on the frequency the VFD is outputting.
Edit: I have a different VFD than you have, and I don't see the Rs- and Rs+ headers on yours.
Edit: I have a different VFD than you have, and I don't see the Rs- and Rs+ headers on yours.
Last edit: 28 Feb 2021 20:03 by kkuehn.
Please Log in or Create an account to join the conversation.
- Hakan
- Offline
- Platinum Member
-
Less
More
- Posts: 1317
- Thank you received: 453
28 Feb 2021 20:45 #200461
by Hakan
Replied by Hakan on topic 2.2kw VFD Spindle wiring to Mesa 7i76e
I agree on Modbus. But it seems from a quick search that the "ver 2" is a clone that lacks Modbus www.kronosrobotics.com/hy02d223b-vfd-type-2
Follow Andy's wiring a few posts back,
where Andy has ACM and DCM you have only GND,
and you have +12V instead of +10
Follow Andy's wiring a few posts back,
where Andy has ACM and DCM you have only GND,
and you have +12V instead of +10
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18020
- Thank you received: 5294
28 Feb 2021 21:07 - 28 Feb 2021 21:08 #200464
by PCW
Replied by PCW on topic 2.2kw VFD Spindle wiring to Mesa 7i76e
Note that modbus may not be as good for spindle synced motion
(especially rigid tapping) since it can have random delays in 10s
to 100s of ms region.
(especially rigid tapping) since it can have random delays in 10s
to 100s of ms region.
Last edit: 28 Feb 2021 21:08 by PCW.
The following user(s) said Thank You: Sadmeatball
Please Log in or Create an account to join the conversation.
Moderators: PCW, jmelson
Time to create page: 0.175 seconds