Thanks for your words.
OK, so you do get the green LED without the SCHP and E-Stop. So, the problem is when you configured and wired e-stop. OK, I am sorry for the confusion on my part. OK, here are some thoughts:
- The idea with this boards, is that you connect the e-stop pin using a high in parallel with the EN terminal, which acts as the hardware enable. So, when e-stop opens, the first thing that happens is that all outputs get disabled. This is at hardware level. Then software gets notified through the e-stop signal of the e-stop condition. The idea behind this is that you do not relay on the software to stop your system, but on the wiring. As a software failure could be one of the reasons why you are pressing the e-stop button.
- If you are wiring like I described above, the common for e-stop and EN must be +5vdc. The same +5vdc that you used in the first place for the EN and the input pin must be set to pull-down. This way when it is in the air, then the input will be a low.
- You can use a multimeter to verify you have the +5vdc on the EN and input pin for e-stop when the switch is closed and to see 0vdc when open.
- Maybe you need to change the active high/low used for e-stop.
- What happens if you move the jumper back on the board to disable the outputs?
Check that and let me know how it goes.
Arturo Duncan
cnc4pc.com