14 Dec 2013 01:07 #41589
by emcPT
Replied by emcPT on topic touch off don't zero the axis
Then something is wrong here.
What I know for sure is that the drive is well tuned as it was tested and tested.
Using the recommendation of PCW we were not able to get a proper working system. Please take a look below for what we had and was working:
and using the PCW recommendation we changed to (only changes are present, the others are the same):
We have immediate following error.
Is the following error in velocity mode, positions or velocity?
What I know for sure is that the drive is well tuned as it was tested and tested.
Using the recommendation of PCW we were not able to get a proper working system. Please take a look below for what we had and was working:
#********************
# Axis Z
#********************
[AXIS_2]
TYPE = LINEAR
HOME = 0.0
FERROR = 10
MIN_FERROR = 5
MAX_VELOCITY = 167
MAX_ACCELERATION = 800
P = 1.0
I = 0.0
D = 0.0
FF0 = 0.0
FF1 = 0.0
FF2 = 0.0
BIAS = 0.0
DEADBAND = 0.0
MAX_OUTPUT = 10
ENCODER_SCALE = -1500
OUTPUT_SCALE = 10
OUTPUT_MIN_LIMIT = -10
OUTPUT_MAX_LIMIT = 10
MIN_LIMIT = -272
MAX_LIMIT = 0
HOME_SEARCH_VEL = 10
HOME_LATCH_VEL = -10
HOME_USE_INDEX = YES
HOME_OFFSET = 0.0
HOME_SEQUENCE = 0
and using the PCW recommendation we changed to (only changes are present, the others are the same):
MAX_VELOCITY = 167
MAX_OUTPUT = 167
OUTPUT_SCALE = 167
OUTPUT_MIN_LIMIT = -167
OUTPUT_MAX_LIMIT = 167
We have immediate following error.
Is the following error in velocity mode, positions or velocity?
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18775
- Thank you received: 5187
14 Dec 2013 01:39 - 14 Dec 2013 01:46 #41592
by PCW
Replied by PCW on topic touch off don't zero the axis
Sure, This is expected (you have 1/16.7 of the former P gain so the servo will probably barely follow the commanded position)
you should go through JTs tuning tutorial:
gnipsel.com/linuxcnc/tuning/servo.html
Note the part where you increase P until you get oscillations and then back off
(You want the highest value of P you can get and still remain stable)
FF1 around 1 should be about right
For a velocity mode drive most of the tuning is just forwarding the
velocity command through the PID loop via FF1
(there is no hope of decent results without using FF1)
you should go through JTs tuning tutorial:
gnipsel.com/linuxcnc/tuning/servo.html
Note the part where you increase P until you get oscillations and then back off
(You want the highest value of P you can get and still remain stable)
FF1 around 1 should be about right
For a velocity mode drive most of the tuning is just forwarding the
velocity command through the PID loop via FF1
(there is no hope of decent results without using FF1)
Last edit: 14 Dec 2013 01:46 by PCW.
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 23377
- Thank you received: 4966
14 Dec 2013 08:40 #41599
by andypugh
Do you have a PID running in LinuxCNC? If you have velocity-mode at the drives and no PID on the LinuxCNC side then I am astonished that it works at all.
Replied by andypugh on topic touch off don't zero the axis
Drives are already at velocity mode.
Do you have a PID running in LinuxCNC? If you have velocity-mode at the drives and no PID on the LinuxCNC side then I am astonished that it works at all.
Please Log in or Create an account to join the conversation.
- emcPT
-
- Offline
- Platinum Member
-
Less
More
- Posts: 702
- Thank you received: 139
18 Dec 2013 05:23 #41714
by emcPT
Replied by emcPT on topic touch off don't zero the axis
To resume what happened, as I do not like to leave open threads and it can help others:
Having :
MAX_VELOCITY = 167
MAX_OUTPUT = 167
OUTPUT_SCALE = 167
OUTPUT_MIN_LIMIT = -167
OUTPUT_MAX_LIMIT = 167
or
MAX_VELOCITY = 10
MAX_OUTPUT = 10
OUTPUT_SCALE = 10
OUTPUT_MIN_LIMIT = -10
OUTPUT_MAX_LIMIT = 10
did not made any difference, except the PID had to be retunned (basically what PCW said was correct: if with the settings = 10; the P=1, testing with the settings = 167, the same result was achieved with P=16.7).
Regarding the PID: It was working relative ok with the P=1 (or with P=16.7). No large difference was noticeable.
Running the halscope and tunne the PID, we managed to lower a bit the following error (FF1 ended to be 0.6) and now we have 0.3mm following error peck at acceleration and deceleration. During the rapids the following error gets near zero. Machine is moving at 10m/min. Motors are enough to move easily the axis.
I was expecting a better result, but we could not improve it.
Having :
MAX_VELOCITY = 167
MAX_OUTPUT = 167
OUTPUT_SCALE = 167
OUTPUT_MIN_LIMIT = -167
OUTPUT_MAX_LIMIT = 167
or
MAX_VELOCITY = 10
MAX_OUTPUT = 10
OUTPUT_SCALE = 10
OUTPUT_MIN_LIMIT = -10
OUTPUT_MAX_LIMIT = 10
did not made any difference, except the PID had to be retunned (basically what PCW said was correct: if with the settings = 10; the P=1, testing with the settings = 167, the same result was achieved with P=16.7).
Regarding the PID: It was working relative ok with the P=1 (or with P=16.7). No large difference was noticeable.
Running the halscope and tunne the PID, we managed to lower a bit the following error (FF1 ended to be 0.6) and now we have 0.3mm following error peck at acceleration and deceleration. During the rapids the following error gets near zero. Machine is moving at 10m/min. Motors are enough to move easily the axis.
I was expecting a better result, but we could not improve it.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18775
- Thank you received: 5187
18 Dec 2013 06:00 #41715
by PCW
Replied by PCW on topic touch off don't zero the axis
was 1 (or 16.7) the highest gain (P) you could achieve without oscillation?
did you try and tune out the spikes on accel with (a small amount) of FF2?
did you try and tune out the spikes on accel with (a small amount) of FF2?
Please Log in or Create an account to join the conversation.
- emcPT
-
- Offline
- Platinum Member
-
Less
More
- Posts: 702
- Thank you received: 139
19 Dec 2013 03:23 #41791
by emcPT
Replied by emcPT on topic touch off don't zero the axis
With all the values at 167, we could increase the P up to 70, starting oscillating near 80. We ended to use around 30, where it oscillates less during fixed velocity, at a cost of a higher setting time.
The FF1 centered the error during movement, and the FF2 changed (but for only a small amount) the fixed error (error is not zero during stop). The title of this thread is the result of the error not be zero when the axis is stopped (in the attachment z_scope.png this is visible). The FF2 did not changed the initial or final spike, and I did a LOT of tests.
Changing the FF3, corrected the "fixed error" but at a high cost of a more jerky movement.
The FF1 centered the error during movement, and the FF2 changed (but for only a small amount) the fixed error (error is not zero during stop). The title of this thread is the result of the error not be zero when the axis is stopped (in the attachment z_scope.png this is visible). The FF2 did not changed the initial or final spike, and I did a LOT of tests.
Changing the FF3, corrected the "fixed error" but at a high cost of a more jerky movement.
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 23377
- Thank you received: 4966
19 Dec 2013 03:27 #41793
by andypugh
I am also a bit surprised to find that I is zero, that is normally useful for removing the last bit of error.
Replied by andypugh on topic touch off don't zero the axis
Did you experiment to see if any D term can damp the oscillation?With all the values at 167, we could increase the P up to 70, starting oscillating near 80.
I am also a bit surprised to find that I is zero, that is normally useful for removing the last bit of error.
The following user(s) said Thank You: emcPT
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18775
- Thank you received: 5187
19 Dec 2013 03:34 - 19 Dec 2013 04:04 #41794
by PCW
Replied by PCW on topic touch off don't zero the axis
FF2 should only affect accelerated motion (its acceleration feed forward for a PID loop that works on position)
so should only affect the error during the ramp-up and ramp-down phase of your jog
What is FF3?
Like Andy says, the I term can be used to remove that last bit of static error,
but proceed with caution, too much I term will lead to instability.
edit:
One more note: what is the time per division? its clipped off in the halscope images
there seems to be significant delay between the command and the start of motion
this may indicate a tuning issue in the drives (command input filter for example)
so should only affect the error during the ramp-up and ramp-down phase of your jog
What is FF3?
Like Andy says, the I term can be used to remove that last bit of static error,
but proceed with caution, too much I term will lead to instability.
edit:
One more note: what is the time per division? its clipped off in the halscope images
there seems to be significant delay between the command and the start of motion
this may indicate a tuning issue in the drives (command input filter for example)
Last edit: 19 Dec 2013 04:04 by PCW.
The following user(s) said Thank You: emcPT
Please Log in or Create an account to join the conversation.
- emcPT
-
- Offline
- Platinum Member
-
Less
More
- Posts: 702
- Thank you received: 139
19 Dec 2013 15:54 #41816
by emcPT
My mistake, when I wrote, I was not on the machine and I had to myself that the values started at 1, so FF1 FF2 and FF3. They were really FF0, FF1 and FF2.
With more tunning, we ended up in using:
P=65
I=2.5 (in one axis) the other 0.7
D=0.2
FF1=0.59
FF2=0.004 (in one axis) the other 0.002
This improved the response and now we have max peck of 1/3 in relation with the previous results AND the actual position on the DRO is near the commanded position as the ferror stationary is near 0.001 mm.
200mSec.
This was quite a nice tip! I am almost sure that the drive input filter is on. Will check it.
Replied by emcPT on topic touch off don't zero the axis
FF2 should only affect accelerated motion (its acceleration feed forward for a PID loop that works on position)
so should only affect the error during the ramp-up and ramp-down phase of your jog
What is FF3?
My mistake, when I wrote, I was not on the machine and I had to myself that the values started at 1, so FF1 FF2 and FF3. They were really FF0, FF1 and FF2.
With more tunning, we ended up in using:
P=65
I=2.5 (in one axis) the other 0.7
D=0.2
FF1=0.59
FF2=0.004 (in one axis) the other 0.002
This improved the response and now we have max peck of 1/3 in relation with the previous results AND the actual position on the DRO is near the commanded position as the ferror stationary is near 0.001 mm.
One more note: what is the time per division? its clipped off in the halscope images
there seems to be significant delay between the command and the start of motion
this may indicate a tuning issue in the drives (command input filter for example)
200mSec.
This was quite a nice tip! I am almost sure that the drive input filter is on. Will check it.
Please Log in or Create an account to join the conversation.
- emcPT
-
- Offline
- Platinum Member
-
Less
More
- Posts: 702
- Thank you received: 139
19 Dec 2013 21:26 #41830
by emcPT
Replied by emcPT on topic touch off don't zero the axis
Done!
The input filter on the drive was making a large difference. We had to readjust all, and the ferror now is minimal. We have the graphs attached!
Thank you. Again.
The input filter on the drive was making a large difference. We had to readjust all, and the ferror now is minimal. We have the graphs attached!
Thank you. Again.
Please Log in or Create an account to join the conversation.