03 Mar 2018 16:06 #106880
by aleksamc
How to connect input and output to MESA 7i76 was created by aleksamc
Dear all forumers,
I have Maxine EP1C driver and there are inputs and outputs are controls with "gnd" voltage. I add pictures from manual.
I have MESA 7i76 card and there to input should come 24V but in manual of the drive to output connects 24V but it not generates them. Should I connect to DO1 of drive DI of messa and to DOCOM - GND? IT will be inverse signal then.
And outputs of MESA should send 24 V but to input of the drive comes gnd. Can I connect to input of the drive - output of mesa 7i76 card? Will it work?
I have Maxine EP1C driver and there are inputs and outputs are controls with "gnd" voltage. I add pictures from manual.
I have MESA 7i76 card and there to input should come 24V but in manual of the drive to output connects 24V but it not generates them. Should I connect to DO1 of drive DI of messa and to DOCOM - GND? IT will be inverse signal then.
And outputs of MESA should send 24 V but to input of the drive comes gnd. Can I connect to input of the drive - output of mesa 7i76 card? Will it work?
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18103
- Thank you received: 5326
03 Mar 2018 17:04 #106881
by PCW
Replied by PCW on topic How to connect input and output to MESA 7i76
Thats bit awkward since the both the drives inputs and outputs work the opposite way as the 7I76s I/O
For 7I76 inputs you can add a stiff (say 2K) pullup resistor
Ror 7I76 outputs you would need to add a relay or OPTO
(or use a 7I76D which has sinking outputs)
For 7I76 inputs you can add a stiff (say 2K) pullup resistor
Ror 7I76 outputs you would need to add a relay or OPTO
(or use a 7I76D which has sinking outputs)
Please Log in or Create an account to join the conversation.
- aleksamc
-
Topic Author
- Offline
- Platinum Member
-
Less
More
- Posts: 569
- Thank you received: 67
05 Mar 2018 15:52 #106959
by aleksamc
Replied by aleksamc on topic How to connect input and output to MESA 7i76
Thank you Peter. I used Relay as you advised.
Please Log in or Create an account to join the conversation.
- garrettmin
-
- Offline
- Senior Member
-
Less
More
- Posts: 60
- Thank you received: 0
21 Mar 2022 19:19 - 21 Mar 2022 20:30 #237946
by garrettmin
Replied by garrettmin on topic How to connect input and output to MESA 7i76
7i76D:
7i92_7i76x1D.bit
Contingencies:
For PNP or NC (Normally Closed) limit/home switches you must connect the
hm2_5i25.0.7i76.0.0.input-XX-not limit/home pin to motions limit/home pins
Contingency Avoid:
Install Normally Open Switches
LinuxCNC:
hm2_7i92.0.7i76.0.0.input-oo
does not exist
Is the compiler error a I/O Pinout Wiring error of Sinking/Sourcing NO/NC? I think the compiler error is failed communications between 7i92/7i76D.
How to compile & find this switch?
7i76D
Inputs = Sinking
Outputs = Sinking
This diagram has 7i76E Inputs = Sinking
Correct? Sinking Inputs are Common = TB1 Field Power Common +24V
7i92_7i76x1D.bit
Contingencies:
For PNP or NC (Normally Closed) limit/home switches you must connect the
hm2_5i25.0.7i76.0.0.input-XX-not limit/home pin to motions limit/home pins
Contingency Avoid:
Install Normally Open Switches
LinuxCNC:
hm2_7i92.0.7i76.0.0.input-oo
does not exist
Is the compiler error a I/O Pinout Wiring error of Sinking/Sourcing NO/NC? I think the compiler error is failed communications between 7i92/7i76D.
How to compile & find this switch?
7i76D
Inputs = Sinking
Outputs = Sinking
This diagram has 7i76E Inputs = Sinking
Correct? Sinking Inputs are Common = TB1 Field Power Common +24V
Last edit: 21 Mar 2022 20:30 by garrettmin.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18103
- Thank you received: 5326
21 Mar 2022 19:40 #237948
by PCW
Replied by PCW on topic How to connect input and output to MESA 7i76
"hm2_7i92.0.7i76.0.0.input-00 does not exist"
means that there is no communication from the
7I92 to the 7I76D's field I/O section.
If you connected 24V to the 7I76D's 5V power connection,
its possible that many of the 5V parts on the 7I76D are damaged
including the ones involved in communication with the field
I/O section.
means that there is no communication from the
7I92 to the 7I76D's field I/O section.
If you connected 24V to the 7I76D's 5V power connection,
its possible that many of the 5V parts on the 7I76D are damaged
including the ones involved in communication with the field
I/O section.
Please Log in or Create an account to join the conversation.
- garrettmin
-
- Offline
- Senior Member
-
Less
More
- Posts: 60
- Thank you received: 0
21 Mar 2022 20:27 #237953
by garrettmin
Replied by garrettmin on topic How to connect input and output to MESA 7i76
Thank You for confirming my Short Circuit of 7i76D will also fail 7i76D I/O.
Tech:
7I76E HAS DIFFERENT VOLTAGE THAN 7I76 @ TB3
7I76E TB3 @ PIN 21,22 = UNREG LOGIC PWR+ IN
7I76D TB3 @ PIN 21,22 = +5V
was for the goal of "Diagnostic 7i76D after Short Circuit @ TB1",
attempt to find the 7i76D I/O Switch & confirm Any of 7i76D is funcitonal whatsoever after Short Circuit TB1.
hm2_7i92.0.7i76.0.0.input-00 does not exist
Confirms the Diagnostic of 7i76D Short Circuit:
7i76D is in Failed after Short Circuit, Input-00 does not exist
Tech:
7I76E HAS DIFFERENT VOLTAGE THAN 7I76 @ TB3
7I76E TB3 @ PIN 21,22 = UNREG LOGIC PWR+ IN
7I76D TB3 @ PIN 21,22 = +5V
- 5V ONLY
- NOT EQUAL TO
- 24V UNREG LOGIC PWR+ IN
- NOT EQUAL TO
was for the goal of "Diagnostic 7i76D after Short Circuit @ TB1",
attempt to find the 7i76D I/O Switch & confirm Any of 7i76D is funcitonal whatsoever after Short Circuit TB1.
hm2_7i92.0.7i76.0.0.input-00 does not exist
Confirms the Diagnostic of 7i76D Short Circuit:
7i76D is in Failed after Short Circuit, Input-00 does not exist
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12156
- Thank you received: 4149
21 Mar 2022 20:54 #237956
by rodw
Replied by rodw on topic How to connect input and output to MESA 7i76
Watch my video
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21980
- Thank you received: 7481
21 Mar 2022 22:24 #237968
by tommylight
What does it report ?
Replied by tommylight on topic How to connect input and output to MESA 7i76
mesaflash --device 5i25 --readhmidPlease Log in or Create an account to join the conversation.