				Im getting my limit switrches setup here and saw this line in the 7i76e manual:
"It is suggested that inputs like limit switches use normally closed switches with one
switch leg connected to field power and the other to the 7I76E input pin, so the normal
machine state (not at limits) is to have the inputs activated. This way, a open switch wire
or wire shorted to ground will cause a detectable machine fault. "
Obviously there is not enough space on feild I/O to connect 2 Limit switches and one home per axis. Should I just use one terminal and distribute from that?
Also running 24v with my sourcing inputs have any issues that require something special like pull up resistors.
Thanks,
					"It is suggested that inputs like limit switches use normally closed switches with one
switch leg connected to field power and the other to the 7I76E input pin, so the normal
machine state (not at limits) is to have the inputs activated. This way, a open switch wire
or wire shorted to ground will cause a detectable machine fault. "
Obviously there is not enough space on feild I/O to connect 2 Limit switches and one home per axis. Should I just use one terminal and distribute from that?
Also running 24v with my sourcing inputs have any issues that require something special like pull up resistors.
Thanks,
Please Log in or Create an account to join the conversation.
- pl7i92
- 
				  
- Offline
- Platinum Member
- 
				  
		Less
		More
		
			
	
		- Posts: 1872
- Thank you received: 358
			
	
						18 May 2019 06:48				#134104
		by pl7i92
	
	
		
			
	
	
		
			
			 		
													
	
				Replied by pl7i92 on topic Some 7i76E questions			
			
					Attachments:
Please Log in or Create an account to join the conversation.
- Mike_Eitel
- 
				  
- Offline
- Platinum Member
- 
				  
		Less
		More
		
			
	
		- Posts: 1052
- Thank you received: 183
			
	
						18 May 2019 09:47				#134141
		by Mike_Eitel
	
	
		
			
	
			
			 		
													
	
				Replied by Mike_Eitel on topic Some 7i76E questions			
			
				In my eyes the detailed capture of each limit switch makes only sense when you can not see the axis. Problem is that it is sometimes not easy to dasychain electronic switches. But you can to chain at least two NC sourcing ones by having vcc supplied by the signal of the first. That should work for 24v and your 7i76e. Maybe even with 4. Worth a tried if you are low with signals.
m5c
Mike
					m5c
Mike
Please Log in or Create an account to join the conversation.
- bevins
- 
				  
- Offline
- Platinum Member
- 
				  
		Less
		More
		
			
	
		- Posts: 1940
- Thank you received: 338
			
	
						18 May 2019 11:39		 -  18 May 2019 11:51		#134171
		by bevins
	
	
		
			
				
Two limit switches for X, two limit switches for Y and one for Z(upper). Share limit switch and home. That's 3 inputs needed. Connect max and min in series Normally closed. So you always have input when not on limit, that way if wire breaks you will know.
					
	
	
			 		
													
	
				Replied by bevins on topic Some 7i76E questions			
			Im getting my limit switrches setup here and saw this line in the 7i76e manual:
"It is suggested that inputs like limit switches use normally closed switches with one
switch leg connected to field power and the other to the 7I76E input pin, so the normal
machine state (not at limits) is to have the inputs activated. This way, a open switch wire
or wire shorted to ground will cause a detectable machine fault. "
Obviously there is not enough space on feild I/O to connect 2 Limit switches and one home per axis. Should I just use one terminal and distribute from that?
Also running 24v with my sourcing inputs have any issues that require something special like pull up resistors.
Thanks,
Two limit switches for X, two limit switches for Y and one for Z(upper). Share limit switch and home. That's 3 inputs needed. Connect max and min in series Normally closed. So you always have input when not on limit, that way if wire breaks you will know.
		Last edit: 18 May 2019 11:51  by bevins.			
			Please Log in or Create an account to join the conversation.
- pl7i92
- 
				  
- Offline
- Platinum Member
- 
				  
		Less
		More
		
			
	
		- Posts: 1872
- Thank you received: 358
			
	
						18 May 2019 11:45				#134175
		by pl7i92
	
	
		
			
	
			
			 		
													
	
				Replied by pl7i92 on topic Some 7i76E questions			
			
				it is the same principal as here
the cherry can take 24V easy so no need to change coltige
			
					the cherry can take 24V easy so no need to change coltige
Please Log in or Create an account to join the conversation.
- Type_Zero_Design
- Offline
- Premium Member
- 
				  
		Less
		More
		
			
	
		- Posts: 133
- Thank you received: 7
			
	
						18 May 2019 13:22				#134182
		by Type_Zero_Design
	
	
		
			
	
			
			 		
													
	
				Replied by Type_Zero_Design on topic Some 7i76E questions			
			
				Hey guys,
Thanks for the info. Just to be clear I'm not asking about the inputs, I have plenty right now.
I was wondering about the feild power output and whether I should do something like pl7i92 suggested, and if that was going to cause any isses
					Thanks for the info. Just to be clear I'm not asking about the inputs, I have plenty right now.
I was wondering about the feild power output and whether I should do something like pl7i92 suggested, and if that was going to cause any isses
Please Log in or Create an account to join the conversation.
- pl7i92
- 
				  
- Offline
- Platinum Member
- 
				  
		Less
		More
		
			
	
		- Posts: 1872
- Thank you received: 358
			
	
						18 May 2019 15:26				#134194
		by pl7i92
	
	
		
			
	
			
			 		
													
	
				Replied by pl7i92 on topic Some 7i76E questions			
			
				the power is the same no matter what clamp it comes from
it is always best to get on Larger mashines
Terminal blocks like 5wise for the GND and + power
as you got so many in out you need to get also some fieldpower terminals
					it is always best to get on Larger mashines
Terminal blocks like 5wise for the GND and + power
as you got so many in out you need to get also some fieldpower terminals