Mesa 5i25 + 7i77 Communication Error
- HalaszAttila
- Offline
- Premium Member
-
Less
More
- Posts: 149
- Thank you received: 5
31 Jul 2019 13:06 #141006
by HalaszAttila
Mesa 5i25 + 7i77 Communication Error was created by HalaszAttila
Hello,
we have a milling machine that runs Linuxcnc over 7 years, with Mesa 5i25 + 7i77 cards.
A few days ago machine starts to give these error messages, for every 10-20 minutes:
After error i restart Linuxcnc and it works more 10-20 minutes.
The messages seems to inform some power supply failure but when i pull out 5VDC connector from MESA 7i77 then i get this messages (that not same from the first photo. Here is a plus Extra Character message).
If i pull out the Field Voltage 24VDC connector from Mesa 7i77 i get these messages (that not the same from the first photo too, here is a Undervoltage extra message).
What you think what this messages from first photo exactly means? And why i get it?
Maybe problem with mesa cards? Unfortunately i dont have other Mesa card to swap it with old, but if someone 100% sure that problem is with cards, i would buy new.
Every power supply is ok, i measure 5,0VDC, and 25,0VDC.
Attila.
we have a milling machine that runs Linuxcnc over 7 years, with Mesa 5i25 + 7i77 cards.
A few days ago machine starts to give these error messages, for every 10-20 minutes:
After error i restart Linuxcnc and it works more 10-20 minutes.
The messages seems to inform some power supply failure but when i pull out 5VDC connector from MESA 7i77 then i get this messages (that not same from the first photo. Here is a plus Extra Character message).
If i pull out the Field Voltage 24VDC connector from Mesa 7i77 i get these messages (that not the same from the first photo too, here is a Undervoltage extra message).
What you think what this messages from first photo exactly means? And why i get it?
Maybe problem with mesa cards? Unfortunately i dont have other Mesa card to swap it with old, but if someone 100% sure that problem is with cards, i would buy new.
Every power supply is ok, i measure 5,0VDC, and 25,0VDC.
Attila.
Attachments:
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18103
- Thank you received: 5326
31 Jul 2019 13:55 #141007
by PCW
Replied by PCW on topic Mesa 5i25 + 7i77 Communication Error
It does look like 5V power issue (since you lose both serial interfaces at once)
Can you monitor the 5V power at the 7I77 (say at an encoder connector) when this happens?
Can you monitor the 5V power at the 7I77 (say at an encoder connector) when this happens?
Please Log in or Create an account to join the conversation.
- HalaszAttila
- Offline
- Premium Member
-
Less
More
- Posts: 149
- Thank you received: 5
31 Jul 2019 14:21 #141009
by HalaszAttila
Replied by HalaszAttila on topic Mesa 5i25 + 7i77 Communication Error
Hm, i suspected that problem is from PSU, therefore i install new (MeanWell 5VDC / 2A) PSU, and change the capacitor and rectifier for 24VDC.
But problem still exist.
Between 5i25 and 7i77 is an ISOL card. Maybe problem is with 5V of PC PSU? But PC and OS works ok.
I will check 5VDC with oscilloscope.
Maybe in encoder cable has a short circuit between 5V and GND... ?
But problem still exist.
Between 5i25 and 7i77 is an ISOL card. Maybe problem is with 5V of PC PSU? But PC and OS works ok.
I will check 5VDC with oscilloscope.
Maybe in encoder cable has a short circuit between 5V and GND... ?
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18103
- Thank you received: 5326
31 Jul 2019 14:28 #141010
by PCW
Replied by PCW on topic Mesa 5i25 + 7i77 Communication Error
Yes, 5V loss on the PC side of the isolator would also cause the same symptoms
so I would check both 5V supplies when you see the issue.
so I would check both 5V supplies when you see the issue.
Please Log in or Create an account to join the conversation.
- svajus123
- Offline
- New Member
-
Less
More
- Posts: 3
- Thank you received: 0
01 Aug 2019 21:11 #141152
by svajus123
Replied by svajus123 on topic Mesa 5i25 + 7i77 Communication Error
7i77-undervoltage fault means that +5v supply voltage level too low on the 7i77 itself.
Assuming that the encoders are fed from the same +5v line-It should be encoder or its damaged wiring fault.
Assuming that the encoders are fed from the same +5v line-It should be encoder or its damaged wiring fault.
Please Log in or Create an account to join the conversation.
- fman
- Offline
- New Member
-
Less
More
- Posts: 1
- Thank you received: 0
03 Aug 2021 21:39 - 03 Aug 2021 21:46 #216867
by fman
Replied by fman on topic Mesa 5i25 + 7i77 Communication Error
Last edit: 03 Aug 2021 21:46 by fman. Reason: picture not appears correctly
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18103
- Thank you received: 5326
03 Aug 2021 22:24 #216869
by PCW
Replied by PCW on topic Mesa 5i25 + 7i77 Communication Error
If you get all those errors, its most likely the there is an issue with the 5I25 card access from the PC.
Either the 3.3V PC motherboard rail is so low that the card has been reset or
there is a contact issue (try removing the 5I25 card, cleaning the PCI contacts and re-installing)
Either the 3.3V PC motherboard rail is so low that the card has been reset or
there is a contact issue (try removing the 5I25 card, cleaning the PCI contacts and re-installing)
Please Log in or Create an account to join the conversation.
Moderators: PCW, jmelson