Hi all,
I have to connect my 7i97 board to analog drives and I have got the board to work by supplying the 5v to the logic part. I feel like the manual is all over the place, 7i77 is mentioned in many places. In the actual 7i77 manual there is TB2 connector where we can connect the field power. In 7i97 we have TB4 where I suppose the field power has to be connected but it is labelled as 5v(I have highlighted it in the attachment). So where should I connect the power to get the required +/- 10 V analog output for the Servo drive SGDA05AS from Yaskawa.
Thanks and Regards,
Shadab
I have to connect my 7i97 board to analog drives and I have got the board to work by supplying the 5v to the logic part. I feel like the manual is all over the place, 7i77 is mentioned in many places. In the actual 7i77 manual there is TB2 connector where we can connect the field power. In 7i97 we have TB4 where I suppose the field power has to be connected but it is labelled as 5v(I have highlighted it in the attachment). So where should I connect the power to get the required +/- 10 V analog output for the Servo drive SGDA05AS from Yaskawa.
Thanks and Regards,
Shadab
Attachments:
Last edit: 02 Sep 2020 07:13 by shadab.
Please Log in or Create an account to join the conversation.
- shadab
-
Topic Author
- Offline
- Junior Member
-
Less
More
- Posts: 39
- Thank you received: 4
02 Sep 2020 09:54 #180407
by shadab
Replied by shadab on topic 7i97 field power wrongly labelled in the manual, where do I supply the power?
After checking the continuities between 5v supply at P3 and the TB4 connector 5v auxiliary input, it shows continuity. The manual is in fact correct. I am still not able to understand how we should supply the power to get the +/- 10v analog drive outputs.
Please Log in or Create an account to join the conversation.
- BeagleBrainz
-
- Visitor
-
02 Sep 2020 11:05 #180411
by BeagleBrainz
Replied by BeagleBrainz on topic 7i97 field power wrongly labelled in the manual, where do I supply the power?
Could a buck\boost converter be on board.
Please Log in or Create an account to join the conversation.
- anfänger
-
- Offline
- Platinum Member
-
Less
More
- Posts: 643
- Thank you received: 262
02 Sep 2020 11:10 #180412
by anfänger
Replied by anfänger on topic 7i97 field power wrongly labelled in the manual, where do I supply the power?
You just apply 5V for Logic and the Volts you need for your IO’s (at my machine this is 24V)
The +-10V are done by the board
The +-10V are done by the board
The following user(s) said Thank You: shadab
Please Log in or Create an account to join the conversation.
- shadab
-
Topic Author
- Offline
- Junior Member
-
Less
More
- Posts: 39
- Thank you received: 4
02 Sep 2020 12:24 #180425
by shadab
Replied by shadab on topic 7i97 field power wrongly labelled in the manual, where do I supply the power?
I got the correct +-10v output thanks.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18103
- Thank you received: 5326
02 Sep 2020 13:35 #180432
by PCW
I only see one mention of 7I77 on page 10 plus I see another error on page 10 (
TB5 mentioned instead of TB3). If you see any other errors I would appreciate
if you could point them out. The 7I97 uses only 5V power, normally applied to P3.
Replied by PCW on topic 7i97 field power wrongly labelled in the manual, where do I supply the power?
Hi all,
I have to connect my 7i97 board to analog drives and I have got the board to work by supplying the 5v to the logic part. I feel like the manual is all over the place, 7i77 is mentioned in many places. In the actual 7i77 manual there is TB2 connector where we can connect the field power. In 7i97 we have TB4 where I suppose the field power has to be connected but it is labelled as 5v(I have highlighted it in the attachment). So where should I connect the power to get the required +/- 10 V analog output for the Servo drive SGDA05AS from Yaskawa.
Thanks and Regards,
Shadab
I only see one mention of 7I77 on page 10 plus I see another error on page 10 (
TB5 mentioned instead of TB3). If you see any other errors I would appreciate
if you could point them out. The 7I97 uses only 5V power, normally applied to P3.
The following user(s) said Thank You: shadab
Please Log in or Create an account to join the conversation.
- shadab
-
Topic Author
- Offline
- Junior Member
-
Less
More
- Posts: 39
- Thank you received: 4
03 Sep 2020 06:21 #180494
by shadab
Replied by shadab on topic 7i97 field power wrongly labelled in the manual, where do I supply the power?
Hi Peter,
Initially it was very confusing because I was comparing it to the 7i77 board. Because mesa does not include any schematic, I was not able to understand the power supply part. Specifically how to 10V is generated. I looked up all the ICs on the board to check whether we have some buck boost DC-DC converter IC on the board or something similar. I connected the PicoScope to the drive output and used your HAL/INI files to generated drive output and was able to do so. I got the correct +-10V as well.
Initially it was very confusing because I was comparing it to the 7i77 board. Because mesa does not include any schematic, I was not able to understand the power supply part. Specifically how to 10V is generated. I looked up all the ICs on the board to check whether we have some buck boost DC-DC converter IC on the board or something similar. I connected the PicoScope to the drive output and used your HAL/INI files to generated drive output and was able to do so. I got the correct +-10V as well.