7i92 + 7i76 + 7i84
- rajsekhar
- Offline
- Elite Member
-
Less
More
- Posts: 206
- Thank you received: 12
14 Aug 2022 02:32 #249689
by rajsekhar
7i92 + 7i76 + 7i84 was created by rajsekhar
I am trying to configure a system with 7i92+7i76+7i84.
This is the first time I am using Mesa.
I have connected the ethernet cable
For 7i92:
As I will use separate power to 7i76, do I need to connect 5V power to 7i92??
I am using parallel port cable having 1:1 connection between DB25 ports (basically home soldered) and not shieled.
For 7i76 & 7i84:
I understand I need to connect 24VDC positive power to TB1 connector (pin 1,2,3,4 daisy chain) and GND to pin 8. Am I right??
should I daisy chain 6,7,8??
This is the first time I am using Mesa.
I have connected the ethernet cable
- computer-7i92
- 7i76RS-422 to 7i84
For 7i92:
As I will use separate power to 7i76, do I need to connect 5V power to 7i92??
I am using parallel port cable having 1:1 connection between DB25 ports (basically home soldered) and not shieled.
For 7i76 & 7i84:
I understand I need to connect 24VDC positive power to TB1 connector (pin 1,2,3,4 daisy chain) and GND to pin 8. Am I right??
should I daisy chain 6,7,8??
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18103
- Thank you received: 5326
14 Aug 2022 02:43 #249691
by PCW
Replied by PCW on topic 7i92 + 7i76 + 7i84
If you are using separate 5V power for the 7I76 you need to supply 5V power to the 7I92 also
(make sure the 7I76 is jumpered to use 5V external power and the 7I92 is jumpered
to NOT supply 5V to the 7I76)
Yes 1,2,3,4 are 24V on the orange field power connector on both the 7I76 and 7I84
(only pin 8 or the orange connector need be connected)
(make sure the 7I76 is jumpered to use 5V external power and the 7I92 is jumpered
to NOT supply 5V to the 7I76)
Yes 1,2,3,4 are 24V on the orange field power connector on both the 7I76 and 7I84
(only pin 8 or the orange connector need be connected)
Please Log in or Create an account to join the conversation.
- rajsekhar
- Offline
- Elite Member
-
Less
More
- Posts: 206
- Thank you received: 12
14 Aug 2022 04:10 #249694
by rajsekhar
Replied by rajsekhar on topic 7i92 + 7i76 + 7i84
in 7i84, there is screw terminals on P5 and no terminals connected to P3.
Should I connect +5VDC to P5 top and GND to P5 bottom??
Should I connect +5VDC to P5 top and GND to P5 bottom??
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18103
- Thank you received: 5326
14 Aug 2022 04:34 #249695
by PCW
Replied by PCW on topic 7i92 + 7i76 + 7i84
Do you mean 7I92?
Yes +5 on the top (this is shown in the 7I92 manual)
Yes +5 on the top (this is shown in the 7I92 manual)
Please Log in or Create an account to join the conversation.
- rajsekhar
- Offline
- Elite Member
-
Less
More
- Posts: 206
- Thank you received: 12
14 Aug 2022 07:26 #249700
by rajsekhar
Replied by rajsekhar on topic 7i92 + 7i76 + 7i84
I completed power connections.
But stuck in Network..I followed this thread
forum.linuxcnc.org/27-driver-boards/3559...ethernet-mesa-boards
but on ping, its a failure. "From 10.10.10.11 icmp_seq=1 Destination Host Unreachable" Refer attached file.
upon terminal command "mesaflash --device 7i92 --addr 10.10.10.10 -readhmid", resulted " No 7i92 board found". Refer attached file.
7i92 connected with 5VDC (4.99 VDC on measurement) power, LED status are as per attached photo and video.
All 7i92 jumpers are in default position.
What to do??
But stuck in Network..I followed this thread
forum.linuxcnc.org/27-driver-boards/3559...ethernet-mesa-boards
but on ping, its a failure. "From 10.10.10.11 icmp_seq=1 Destination Host Unreachable" Refer attached file.
upon terminal command "mesaflash --device 7i92 --addr 10.10.10.10 -readhmid", resulted " No 7i92 board found". Refer attached file.
7i92 connected with 5VDC (4.99 VDC on measurement) power, LED status are as per attached photo and video.
All 7i92 jumpers are in default position.
What to do??
Please Log in or Create an account to join the conversation.
- Clive S
- Offline
- Platinum Member
-
Less
More
- Posts: 2204
- Thank you received: 486
14 Aug 2022 07:37 - 14 Aug 2022 07:41 #249702
by Clive S
Replied by Clive S on topic 7i92 + 7i76 + 7i84
I think the default I.P. is in the 192.168.1.121 ish
So you have to set the jumper to the 10.10.10.10 range (its is shown in the manual)
W6 should be up
www.mesanet.com/pdf/parallel/7i92man.pdf
So you have to set the jumper to the 10.10.10.10 range (its is shown in the manual)
W6 should be up
www.mesanet.com/pdf/parallel/7i92man.pdf
Last edit: 14 Aug 2022 07:41 by Clive S.
Please Log in or Create an account to join the conversation.
- rajsekhar
- Offline
- Elite Member
-
Less
More
- Posts: 206
- Thank you received: 12
14 Aug 2022 08:08 #249704
by rajsekhar
Replied by rajsekhar on topic 7i92 + 7i76 + 7i84
Thank you. W6 made Up and problem solved. Its pinging, attached photo. Hope it is ok.
Another query:
7i92 is connected by DB25 cable to 7i76 and 7i76RS422 connected to 7i84.
What else networking to be setup for 7i76 & 7i84??
Another query:
7i92 is connected by DB25 cable to 7i76 and 7i76RS422 connected to 7i84.
What else networking to be setup for 7i76 & 7i84??
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21980
- Thank you received: 7480
14 Aug 2022 10:11 #249707
by tommylight
Replied by tommylight on topic 7i92 + 7i76 + 7i84
No more networking, it is all good.
Use mesaflash to check what firmware is on the 7i92, you might need to flash the firmware for 7i92/7i76.
7i84 does not need any flashing or setup except maybe activating the SSerial port in the hal file.
Use mesaflash to check what firmware is on the 7i92, you might need to flash the firmware for 7i92/7i76.
7i84 does not need any flashing or setup except maybe activating the SSerial port in the hal file.
Please Log in or Create an account to join the conversation.
- rajsekhar
- Offline
- Elite Member
-
Less
More
- Posts: 206
- Thank you received: 12
14 Aug 2022 11:42 #249710
by rajsekhar
Replied by rajsekhar on topic 7i92 + 7i76 + 7i84
the terminal emulator data as follows:
============
raycnc1@debian:~$ mesaflash --device 7i92 --addr 10.10.10.10 --readhmid
Configuration Name: HOSTMOT2
General configuration information:
BoardName : MESA7I92
FPGA Size: 9 KGates
FPGA Pins: 144
Number of IO Ports: 2
Width of one I/O port: 17
Clock Low frequency: 100.0000 MHz
Clock High frequency: 200.0000 MHz
IDROM Type: 3
Instance Stride 0: 4
Instance Stride 1: 64
Register Stride 0: 256
Register Stride 1: 256
Modules in configuration:
Module: DPLL
There are 1 of DPLL in configuration
Version: 0
Registers: 7
BaseAddress: 7000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: WatchDog
There are 1 of WatchDog in configuration
Version: 0
Registers: 3
BaseAddress: 0C00
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: IOPort
There are 2 of IOPort in configuration
Version: 0
Registers: 5
BaseAddress: 1000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: QCount
There are 1 of QCount in configuration
Version: 2
Registers: 5
BaseAddress: 3000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: SSerial
There are 1 of SSerial in configuration
Version: 0
Registers: 6
BaseAddress: 5B00
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 64 bytes
Module: StepGen
There are 5 of StepGen in configuration
Version: 2
Registers: 10
BaseAddress: 2000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: LED
There are 1 of LED in configuration
Version: 0
Registers: 1
BaseAddress: 0200
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Configuration pin-out:
IO Connections for P2
Pin# I/O Pri. func Sec. func Chan Pin func Pin Dir
1 0 IOPort StepGen 0 Dir/Table2 (Out)
14 1 IOPort StepGen 0 Step/Table1 (Out)
2 2 IOPort StepGen 1 Dir/Table2 (Out)
15 3 IOPort StepGen 1 Step/Table1 (Out)
3 4 IOPort StepGen 2 Dir/Table2 (Out)
16 5 IOPort StepGen 2 Step/Table1 (Out)
4 6 IOPort StepGen 3 Dir/Table2 (Out)
17 7 IOPort StepGen 3 Step/Table1 (Out)
5 8 IOPort StepGen 4 Dir/Table2 (Out)
6 9 IOPort StepGen 4 Step/Table1 (Out)
7 10 IOPort SSerial 0 TXData0 (Out)
8 11 IOPort SSerial 0 RXData0 (In)
9 12 IOPort SSerial 0 TXData1 (Out)
10 13 IOPort SSerial 0 RXData1 (In)
11 14 IOPort QCount 0 Quad-IDX (In)
12 15 IOPort QCount 0 Quad-B (In)
13 16 IOPort QCount 0 Quad-A (In)
IO Connections for P1
Pin# I/O Pri. func Sec. func Chan Pin func Pin Dir
1 17 IOPort None
14 18 IOPort None
2 19 IOPort None
15 20 IOPort None
3 21 IOPort None
16 22 IOPort None
4 23 IOPort None
17 24 IOPort None
5 25 IOPort None
6 26 IOPort None
7 27 IOPort None
8 28 IOPort None
9 29 IOPort None
10 30 IOPort None
11 31 IOPort None
12 32 IOPort None
13 33 IOPort None
=======================================
it is clear that P2 connector is configured. I am forwarding towards stepper connections.
============
raycnc1@debian:~$ mesaflash --device 7i92 --addr 10.10.10.10 --readhmid
Configuration Name: HOSTMOT2
General configuration information:
BoardName : MESA7I92
FPGA Size: 9 KGates
FPGA Pins: 144
Number of IO Ports: 2
Width of one I/O port: 17
Clock Low frequency: 100.0000 MHz
Clock High frequency: 200.0000 MHz
IDROM Type: 3
Instance Stride 0: 4
Instance Stride 1: 64
Register Stride 0: 256
Register Stride 1: 256
Modules in configuration:
Module: DPLL
There are 1 of DPLL in configuration
Version: 0
Registers: 7
BaseAddress: 7000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: WatchDog
There are 1 of WatchDog in configuration
Version: 0
Registers: 3
BaseAddress: 0C00
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: IOPort
There are 2 of IOPort in configuration
Version: 0
Registers: 5
BaseAddress: 1000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: QCount
There are 1 of QCount in configuration
Version: 2
Registers: 5
BaseAddress: 3000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: SSerial
There are 1 of SSerial in configuration
Version: 0
Registers: 6
BaseAddress: 5B00
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 64 bytes
Module: StepGen
There are 5 of StepGen in configuration
Version: 2
Registers: 10
BaseAddress: 2000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: LED
There are 1 of LED in configuration
Version: 0
Registers: 1
BaseAddress: 0200
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Configuration pin-out:
IO Connections for P2
Pin# I/O Pri. func Sec. func Chan Pin func Pin Dir
1 0 IOPort StepGen 0 Dir/Table2 (Out)
14 1 IOPort StepGen 0 Step/Table1 (Out)
2 2 IOPort StepGen 1 Dir/Table2 (Out)
15 3 IOPort StepGen 1 Step/Table1 (Out)
3 4 IOPort StepGen 2 Dir/Table2 (Out)
16 5 IOPort StepGen 2 Step/Table1 (Out)
4 6 IOPort StepGen 3 Dir/Table2 (Out)
17 7 IOPort StepGen 3 Step/Table1 (Out)
5 8 IOPort StepGen 4 Dir/Table2 (Out)
6 9 IOPort StepGen 4 Step/Table1 (Out)
7 10 IOPort SSerial 0 TXData0 (Out)
8 11 IOPort SSerial 0 RXData0 (In)
9 12 IOPort SSerial 0 TXData1 (Out)
10 13 IOPort SSerial 0 RXData1 (In)
11 14 IOPort QCount 0 Quad-IDX (In)
12 15 IOPort QCount 0 Quad-B (In)
13 16 IOPort QCount 0 Quad-A (In)
IO Connections for P1
Pin# I/O Pri. func Sec. func Chan Pin func Pin Dir
1 17 IOPort None
14 18 IOPort None
2 19 IOPort None
15 20 IOPort None
3 21 IOPort None
16 22 IOPort None
4 23 IOPort None
17 24 IOPort None
5 25 IOPort None
6 26 IOPort None
7 27 IOPort None
8 28 IOPort None
9 29 IOPort None
10 30 IOPort None
11 31 IOPort None
12 32 IOPort None
13 33 IOPort None
=======================================
it is clear that P2 connector is configured. I am forwarding towards stepper connections.
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21980
- Thank you received: 7480
14 Aug 2022 21:53 #249741
by tommylight
Replied by tommylight on topic 7i92 + 7i76 + 7i84
Moved to "driver boards".
-
Not sure but to me it looks like the firmware is OK for 7i76.
Use PncConf or JT's MesaCT tool to create a simple config so you can start LinuxCNC and check if everything is working.
-
Not sure but to me it looks like the firmware is OK for 7i76.
Use PncConf or JT's MesaCT tool to create a simple config so you can start LinuxCNC and check if everything is working.
Please Log in or Create an account to join the conversation.
Moderators: PCW, jmelson
Time to create page: 1.947 seconds