7i84 Analog inputs
- nwallace
- Offline
- Senior Member
-
Less
More
- Posts: 60
- Thank you received: 5
12 Sep 2023 01:50 #280511
by nwallace
7i84 Analog inputs was created by nwallace
I am looking to do spindle, feed and rapid override via potentiometers. I have a 7i84 that I can use. It says the inputs 0-3 can be used for analog inputs. I am looking for a little guidance on how that would be wired as well as how the HAL should work. Has anyone done this before? I was unable to find anything helpful in my searching on the forum.
Please Log in or Create an account to join the conversation.
- nwallace
- Offline
- Senior Member
-
Less
More
- Posts: 60
- Thank you received: 5
12 Sep 2023 17:21 #280567
by nwallace
Replied by nwallace on topic 7i84 Analog inputs
Figured out the HAL required to get the analog inputs to show. I just needed to change the "sserial_port_0=0xxxxxxx" config option in the hm2_eth line to "sserial_port_0=1xxxxxxx".
Please Log in or Create an account to join the conversation.
- tommylight
-
- Online
- Moderator
-
Less
More
- Posts: 20174
- Thank you received: 6864
13 Sep 2023 12:30 #280630
by tommylight
Replied by tommylight on topic 7i84 Analog inputs
Sorry, i did read this and left it open to reply and went on to check other topics while the reply page loads, and had timeouts and ......
Glad you figured it out.
Glad you figured it out.
Please Log in or Create an account to join the conversation.
- nwallace
- Offline
- Senior Member
-
Less
More
- Posts: 60
- Thank you received: 5
21 Sep 2023 02:53 - 21 Sep 2023 03:17 #281273
by nwallace
Replied by nwallace on topic 7i84 Analog inputs
I am now having an issue with the voltage not being linear even though I am using 50k linear pots. I assume this is because of my lack of electronics knowledge and some basic thing that I don't know. See the attached graph. I am using a 36v supply with the positive connected to the first pin of the pot, negative to the third pin and the input on the 7i84 connected to the wiper. I understand the dead zone on either end of the graph but I don't understand why it isn't pretty close to a straight line. I divided the ~300 degree rotation into 16 points. Here are the actual values:
1 - 0
2 - 0
3 - 1.850588
4 - 3.131765
5 - 4.128235
6 - 5.124706
7 - 5.978823
8 - 7.117647
9 - 8.683529
10 - 10.10706
11 - 11.95765
12 - 15.23176
13 - 19.50235
14 - 27.33176
15 - 36.01529
16 - 36.01529
Everything seems good enough until around points 10 or 11. Then the voltage shoots up significantly. Center on these pots reads about 7.9v.
I would appreciate guidance from anyone who knows what's going on here.
1 - 0
2 - 0
3 - 1.850588
4 - 3.131765
5 - 4.128235
6 - 5.124706
7 - 5.978823
8 - 7.117647
9 - 8.683529
10 - 10.10706
11 - 11.95765
12 - 15.23176
13 - 19.50235
14 - 27.33176
15 - 36.01529
16 - 36.01529
Everything seems good enough until around points 10 or 11. Then the voltage shoots up significantly. Center on these pots reads about 7.9v.
I would appreciate guidance from anyone who knows what's going on here.
Last edit: 21 Sep 2023 03:17 by nwallace. Reason: Correct degrees of rotation
Please Log in or Create an account to join the conversation.
- nwallace
- Offline
- Senior Member
-
Less
More
- Posts: 60
- Thank you received: 5
21 Sep 2023 03:20 - 21 Sep 2023 03:21 #281275
by nwallace
Replied by nwallace on topic 7i84 Analog inputs
The pots I have are these:
2 - PDB181-K220K-503B (50k linear pot with center detent)
1 - PDB181-K415K-503B (50k linear pot)
I have attached the datasheet.
2 - PDB181-K220K-503B (50k linear pot with center detent)
1 - PDB181-K415K-503B (50k linear pot)
I have attached the datasheet.
Last edit: 21 Sep 2023 03:21 by nwallace.
Please Log in or Create an account to join the conversation.
- tommylight
-
- Online
- Moderator
-
Less
More
- Posts: 20174
- Thank you received: 6864
21 Sep 2023 10:45 #281289
by tommylight
Replied by tommylight on topic 7i84 Analog inputs
Pot has 3 pins, middle pin to mesa input, one side pin to GND the other side pin to +24V or 12V or whatever you are using.
Also, check if they are ok with a DVM, see if the resistance is linear, if not, use another pot.
Also, check if they are ok with a DVM, see if the resistance is linear, if not, use another pot.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18531
- Thank you received: 5079
21 Sep 2023 14:01 - 21 Sep 2023 14:23 #281315
by PCW
Replied by PCW on topic 7i84 Analog inputs
This behaviour is expected because the input impedance of the 7I84
is about 11 K ohms. A 50K ohm pot has an equivalent source
impedance of close to 0 ohms at either end, but 12.5K ohm source
impedance in the middle of its range. This means at 1/2 way up
the 50K Ohm pot looks like a 18V source with 12.5K of series resistance.
The means the reading in in middle of the range will be less than
1/2 the expected linear reading.
I would probably use 24V and a 5K pot.
is about 11 K ohms. A 50K ohm pot has an equivalent source
impedance of close to 0 ohms at either end, but 12.5K ohm source
impedance in the middle of its range. This means at 1/2 way up
the 50K Ohm pot looks like a 18V source with 12.5K of series resistance.
The means the reading in in middle of the range will be less than
1/2 the expected linear reading.
I would probably use 24V and a 5K pot.
Last edit: 21 Sep 2023 14:23 by PCW.
The following user(s) said Thank You: tommylight, nwallace