Perfect! Thanks!I assume you're running a separate spindle - like a Bosch Colt or some other manually-activated thing? Otherwise it's not really a router...?
If you want to add a filter you can add it to the AC-in between the main circuit breaker and a distribution block (that your PSU's are fed from).
Unless you have some component that generates PWM noise, I don't see a need for an EMI filter or line reactor with the setup you've described.
For surge protection, don't bother. The PSU's will take the hit and likely save your drives and other components. You're better off spending time/money making sure you've got a good e-stop circuit and disconnect scheme.
Please Log in or Create an account to join the conversation.
Please Log in or Create an account to join the conversation.
Actually maybe I described what I was doing incorrectly. I am running 120V mainly because getting 240V to my machine at this time would be a hassle. What I meant is that I have two open spots (120V) in my electrical panel that I plan to run a dedicated 20A circuit to my CNC. The circuit that is currently in my CNC room is used by other shop tools/machinery (miter saw, table saw, drill, planer, LinuxCNC PC, etc). My thought was to run two separate circuits in order to hopefully provide cleaner power to the logic/low voltage side, but looks like that is not the case, but also I don't want to take the chance of tripping the breaker if I happen to over load the circuit while the CNC is running. If my thinking is incorrect, please let me know.Meant to ask... is there some reason you're going with a 120v system and not 240v? Your PSU's should have a 120/240 switch to take different input voltages.
Going with 240 means a single cord/cable feeding the whole thing rather than two 120v cords (if I'm following your plan).
And if you're worried about where to plug the spindle motor in, if you use a 4-conductor cable from the outlet you can have a neutral line tied to your main house box... meaning you can install a 120v socket on the side of the CNC control box and plug the spindle in to that. One leg of the 240 feeds the socket and return via the neutral. (4-conductor = L1, L2, N, Gnd)
Even better - have that socket controlled by a relay, with the relay coil tied in to your e-stop and/or mesa so you and LCNC can kill the power to the spindle motor socket during an emergency.
I understand using 120 for some systems... I'm doing an old Torchmate right now and using 120 for all the motion & control stuff so it can be plugged in anywhere. But this is a special-use project.
Please Log in or Create an account to join the conversation.