Thx for your time first, i really appreciate your attention.
We have frequent inrush current issues with "B" rated breakers inhouse. our house electricians refused to put slower breakers.
So tripping goes down from my Controllber P3 (10A C-rated) then my Lab breaker (16A B-Rated) and the first house breaker ( 16A -B-Rated). All together. No FI t(guess RCCB in english) tripping, of course - walk of shame when it tripps. This ratings define how fast breakers trip A-B-C-D (not sure if you have this in US?
Old Powerbox was 110/230 mostly with 20A Fuses no breakers, a schütz for Vacuum else nothing special.
For now i just run the motor driver without Mesa Fieldbus and Logic Power
Checked the old setup in it was almost the same, also a very standard SSR to switch, but two NTC's instead of the P1 Current Limiter.
DC currents are super low as there is no torque on the motors.
Thanks for your thought on backfeeding the toroid from the motors/Caps, this should not be possible right?
@tommylight
On the test setup the ssr is controlled by the red emergency button. This failures were mostly driven by switching via the ssr. Might be an issue switching when driver is still enabled. On Linux enabling works fine as you described.
The machine just had homing switches no min/max switches. The servo loop worked fine so far, inhibit/fault seem also ok Z-Axis has a break, X,Y run out when driver gets disabled. But thanks, about the mosfet info . So i should put relays in between PSU and driver not! controlled by LinuxCNC?
@rmu
Also thx for your comments. My understanding so far: The primary side of the toroid induces a voltage peak when turning it off. Maybe together with a high current? it flows backwards through the breakers. But how when switched off? The SSR must be faulty or too slow. Or only half of the sine is switched, one mosfet broken? Ok the Voltage kills the ssr, the current tripps breakers. With a mechanic switch there should be no way to flow back. But i liked the ssr

And what i understand from your comments the secondary side has nothing to do with these issues. That helps.
The "Einschaltstrombegrenzer"- nice German

should not have any effect as it should be switched through at the time.
Thought of using a NTC instead (switches with heat), not sure.
The safety issues are an ongoing issue in our lab.
We mostly do 3D landscapes on prototyping foam aka Sika stock is up to 300mm. We were forced to get a new filter extraction. Even though we hardly catch the chips/dust at the tip as any hose close would mostly hit the stock. Also the machine is open on all sides - an issue - we separated the mill with a thicker curtain (transparent plastic) from the operator - what i am testing now is steel wire around the machine connected to estop switch (picture). Nothing which complies with safety standards - we also have a small robot standing around which is even worse