10 Jan 2019 16:34 #123909
by bevins
MPG 7i76 mesa was created by bevins
Please Log in or Create an account to join the conversation.
- Todd Zuercher
-
- Offline
- Platinum Member
-
Less
More
- Posts: 4785
- Thank you received: 1476
10 Jan 2019 16:46 #123911
by Todd Zuercher
Replied by Todd Zuercher on topic MPG 7i76 mesa
yep
Please Log in or Create an account to join the conversation.
- bevins
-
Topic Author
- Offline
- Platinum Member
-
Less
More
- Posts: 1947
- Thank you received: 338
16 Jan 2019 16:21 - 16 Jan 2019 16:49 #124293
by bevins
Replied by bevins on topic MPG 7i76 mesa
When I tie the 0v to field power gnd It ceases to work. no error and when I restart linuxcnc I get no 5i25 in HAL calibration., but linuxcnc still starts up and when I neable drive nothing happens. This is really bizarre, linuxcnc should spit an error when it doesnt see the 5i25.
The mpg I cannot to count properly anyway. So I tried tieing the gnd 5 v to field power ground and it doesn't like it.,
IT has me on this one.
The mpg I cannot to count properly anyway. So I tried tieing the gnd 5 v to field power ground and it doesn't like it.,
IT has me on this one.
Last edit: 16 Jan 2019 16:49 by bevins.
Please Log in or Create an account to join the conversation.
- bevins
-
Topic Author
- Offline
- Platinum Member
-
Less
More
- Posts: 1947
- Thank you received: 338
16 Jan 2019 16:55 #124295
by bevins
Replied by bevins on topic MPG 7i76 mesa
I'll try connecting field power 12vdc and see if I get 2.5-5 out of the mpg
Please Log in or Create an account to join the conversation.
- bevins
-
Topic Author
- Offline
- Platinum Member
-
Less
More
- Posts: 1947
- Thank you received: 338
16 Jan 2019 16:57 #124296
by bevins
Replied by bevins on topic MPG 7i76 mesa
Without any hal connections, I should still see it count with the enc correct?
Please Log in or Create an account to join the conversation.
- bevins
-
Topic Author
- Offline
- Platinum Member
-
Less
More
- Posts: 1947
- Thank you received: 338
16 Jan 2019 17:39 #124299
by bevins
Replied by bevins on topic MPG 7i76 mesa
I got it working with 12vdc. I guess the 5v is too close to the 2.5 threshold.
Anyway enc1 is counting.
Anyway enc1 is counting.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18091
- Thank you received: 5324
16 Jan 2019 17:58 #124300
by PCW
Replied by PCW on topic MPG 7i76 mesa
The 7I76 MPG inputs are 2.5V nominal but have 10% hysteresis so
must be driven above 3V and below 2V to operate correctly
must be driven above 3V and below 2V to operate correctly
The following user(s) said Thank You: bevins
Please Log in or Create an account to join the conversation.
- bevins
-
Topic Author
- Offline
- Platinum Member
-
Less
More
- Posts: 1947
- Thank you received: 338
16 Jan 2019 19:52 #124301
by bevins
Is that with all the encoder inputs on the 7i76?
Will it take 12volt pulses? Cause with my thc the encoding is not really stable. I am thinking it is not reaching the threshold all the time.
Replied by bevins on topic MPG 7i76 mesa
The 7I76 MPG inputs are 2.5V nominal but have 10% hysteresis so
must be driven above 3V and below 2V to operate correctly
Is that with all the encoder inputs on the 7i76?
Will it take 12volt pulses? Cause with my thc the encoding is not really stable. I am thinking it is not reaching the threshold all the time.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18091
- Thank you received: 5324
16 Jan 2019 20:36 - 16 Jan 2019 20:37 #124303
by PCW
Replied by PCW on topic MPG 7i76 mesa
No, the standard 7I76 (high speed) encoder input is 5V only
If set for TTL mode, the input threshold is 1.6V.
If set for differential mode, the input threshold is ~200 mV differential
with a -7 to +12V common mode range. The THC has differential outputs
and should normally be used with a differential encoder input
(and will drive about differential 3V into the terminated encoder inputs)
If set for TTL mode, the input threshold is 1.6V.
If set for differential mode, the input threshold is ~200 mV differential
with a -7 to +12V common mode range. The THC has differential outputs
and should normally be used with a differential encoder input
(and will drive about differential 3V into the terminated encoder inputs)
Last edit: 16 Jan 2019 20:37 by PCW.