Hi together,
on my second LinuxCNC build now. A good step from No-Name Steppers to a Delta A3 Servo System.
During the selection of the system I must have missed one difference from the Delta A2 to the A3 Servo models.
The A3 series seems to only accept 3,3V differential signals, compared to the A2 - which accepted 5V for it.
What would be the best way to output 3,3V signals?
- Using Bidirectional Logic Level Shifters like a TXB0108
- Access 3,3V from the FPGA directly - could not come up with a way about the how jet
Thanks in advance
Friedrich
on my second LinuxCNC build now. A good step from No-Name Steppers to a Delta A3 Servo System.
During the selection of the system I must have missed one difference from the Delta A2 to the A3 Servo models.
The A3 series seems to only accept 3,3V differential signals, compared to the A2 - which accepted 5V for it.
What would be the best way to output 3,3V signals?
- Using Bidirectional Logic Level Shifters like a TXB0108
- Access 3,3V from the FPGA directly - could not come up with a way about the how jet
Thanks in advance
Friedrich
Please Log in or Create an account to join the conversation.
- tommylight
-
- Away
- Moderator
-
Less
More
- Posts: 21906
- Thank you received: 7465
05 Jun 2021 22:28 #211256
by tommylight
Replied by tommylight on topic Mesa 7i76e - 3.3v Step Output - Delta A3
Use a resistor for each signal wire, but since the current draw is not known, start with two 10KO resistors on the step side and see if you get movement, if not go lower value.
Be aware that a resistor per signal wire is a must on differential inputs.
Be aware that a resistor per signal wire is a must on differential inputs.
Please Log in or Create an account to join the conversation.
- rollfree
- Offline
- Senior Member
-
Less
More
- Posts: 59
- Thank you received: 11
06 Jun 2021 00:03 - 06 Jun 2021 00:03 #211260
by rollfree
A standard line-driver output controller (RS-422) under the load of the receiver usually gives a differential voltage of just around 3.5V.
However, if you want to limit the input current to the driver input for safety, use a limiting resistor. According to the picture in the ASDA-A3 Series User Manual, 2 pieces of 51R resistors in series are used at the input. This would mean a current of around 24mA at a differential voltage of 3.5V and a drop 1V on LED in optocoupler. Reliable safe current is 20mA. So if you want to use a 5V line driver, use a limiting resistor of approx 100R at the driver input.
Replied by rollfree on topic Mesa 7i76e - 3.3v Step Output - Delta A3
I think the subject of the note is the information that 24V communication should not be used. Not that you don't use a normal 5V line-driver output.Hi together,
The A3 series seems to only accept 3,3V differential signals, compared to the A2 - which accepted 5V for it.
A standard line-driver output controller (RS-422) under the load of the receiver usually gives a differential voltage of just around 3.5V.
However, if you want to limit the input current to the driver input for safety, use a limiting resistor. According to the picture in the ASDA-A3 Series User Manual, 2 pieces of 51R resistors in series are used at the input. This would mean a current of around 24mA at a differential voltage of 3.5V and a drop 1V on LED in optocoupler. Reliable safe current is 20mA. So if you want to use a 5V line driver, use a limiting resistor of approx 100R at the driver input.
Last edit: 06 Jun 2021 00:03 by rollfree.
Please Log in or Create an account to join the conversation.
- PCW
-
- Away
- Moderator
-
Less
More
- Posts: 18084
- Thank you received: 5317
06 Jun 2021 00:30 #211263
by PCW
Replied by PCW on topic Mesa 7i76e - 3.3v Step Output - Delta A3
You don't need much, the differential output resistance of the 7I76E is already about 80 Ohms, adding an external 100 Ohm resistor would give you about 14 mA.
Please Log in or Create an account to join the conversation.
- Ritterchen
- Offline
- Junior Member
-
Less
More
- Posts: 34
- Thank you received: 18
07 Jul 2021 13:08 #213967
by Ritterchen
Replied by Ritterchen on topic Mesa 7i76e - 3.3v Step Output - Delta A3
Thank you for all the replies here!
I am not that deep into the electronics (yet) - the hint with the output resistance together with the reference helped me a lot.
With a 100ohm resistor it runs at 12mA, without at 17mA looks good enough to use it without the resistors in between.
Thanks again
I am not that deep into the electronics (yet) - the hint with the output resistance together with the reference helped me a lot.
With a 100ohm resistor it runs at 12mA, without at 17mA looks good enough to use it without the resistors in between.
Thanks again