7i96s Arc Voltage + Encoder Fault
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21797
- Thank you received: 7447
08 Jan 2025 23:23 #318478
by tommylight
-
The THCAD should be wired at the rectifier, not at the plasma output.
And yes, i have a THACD10 wired directly at the output lugs on an inverter plasma, but i would never advise that.
-
Just to be clear, yes you can mount the THCAD inside the plasma source, but absolutely should be avoided by inexperienced members of the human race.
The plasma source has a plethora of warnings plastered all over it, and the manuals spend several pages describing just how dangerous those things are.
Replied by tommylight on topic 7i96s Arc Voltage + Encoder Fault
As i understood, he had 0V before firing the torch, and after the first firing it drops to -45, that absolutely points to THCAD working prior to firing and fails miserably after the firing as be it THACD output or 7i96S inputs are gone from the huge amount of EMI the actual torch firing causes and THCAD being enclosed inside a metal case where the source of all that EMI is.But as PCW says, seeing 0 volt and 45 volts indicates it is working.
-
The THCAD should be wired at the rectifier, not at the plasma output.
And yes, i have a THACD10 wired directly at the output lugs on an inverter plasma, but i would never advise that.
-
Just to be clear, yes you can mount the THCAD inside the plasma source, but absolutely should be avoided by inexperienced members of the human race.
The plasma source has a plethora of warnings plastered all over it, and the manuals spend several pages describing just how dangerous those things are.
The following user(s) said Thank You: rodw, sharp_reaper
Please Log in or Create an account to join the conversation.
- sharp_reaper
- Offline
- Senior Member
-
Less
More
- Posts: 73
- Thank you received: 7
09 Jan 2025 10:47 - 09 Jan 2025 10:47 #318530
by sharp_reaper
Replied by sharp_reaper on topic 7i96s Arc Voltage + Encoder Fault
Thank you for your advice!
The THCAD is mounted inside of the plasma source near the control board.
I'm making the recommended change for a plastic box outside of the plasma source.
This is the first Thermal Dynamics equipment that I work.
I've worked with several Hyperthem plasma cutting systems. All of those got an THCAD inside working well.
The THCAD boards seems to be fine. I have to check the encoder inputs from 7i96s but appears to be usable.
I am making that change to the future plasma systems to guarantee the best care for the boards.
When I have the chance I will make the changes and update you.
Thanks
The THCAD is mounted inside of the plasma source near the control board.
I'm making the recommended change for a plastic box outside of the plasma source.
This is the first Thermal Dynamics equipment that I work.
I've worked with several Hyperthem plasma cutting systems. All of those got an THCAD inside working well.
The THCAD boards seems to be fine. I have to check the encoder inputs from 7i96s but appears to be usable.
I am making that change to the future plasma systems to guarantee the best care for the boards.
When I have the chance I will make the changes and update you.
Thanks
Last edit: 09 Jan 2025 10:47 by sharp_reaper.
Please Log in or Create an account to join the conversation.
- sharp_reaper
- Offline
- Senior Member
-
Less
More
- Posts: 73
- Thank you received: 7
09 Jan 2025 15:40 #318549
by sharp_reaper
Replied by sharp_reaper on topic 7i96s Arc Voltage + Encoder Fault
So I was able to double check for short/faulty cables on P1. I've disconnect the encoder connector from 7i96s and no contact to GND.
Made the change of the location of the THCAD board to the outside of the plasma source in a plastic box.
Connected the shield only on the 7i96s side in the pin TB2.9 with the GND cable.
When I turn on QTPlasmaC the value of Arc Voltage is 145.
The encoder velocity pin seems to be working fine on halshow.
What you recommend to do?
Thanks in advance, really don't understand what's happening.
Made the change of the location of the THCAD board to the outside of the plasma source in a plastic box.
Connected the shield only on the 7i96s side in the pin TB2.9 with the GND cable.
When I turn on QTPlasmaC the value of Arc Voltage is 145.
The encoder velocity pin seems to be working fine on halshow.
What you recommend to do?
Thanks in advance, really don't understand what's happening.
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21797
- Thank you received: 7447
09 Jan 2025 18:44 #318560
by tommylight
When checking encoder velocity, does the value move up(or down?) consistently? Not jumping values?
Replied by tommylight on topic 7i96s Arc Voltage + Encoder Fault
Shield should be wired to control box ground, not Mesa board.Connected the shield only on the 7i96s side in the pin TB2.9 with the GND cable.
When checking encoder velocity, does the value move up(or down?) consistently? Not jumping values?
The following user(s) said Thank You: sharp_reaper
Please Log in or Create an account to join the conversation.
- sharp_reaper
- Offline
- Senior Member
-
Less
More
- Posts: 73
- Thank you received: 7
10 Jan 2025 11:12 #318628
by sharp_reaper
Replied by sharp_reaper on topic 7i96s Arc Voltage + Encoder Fault
Ok, PCW was telling that should be terminated at 7i96s. Can make that change.
The encoder velocity has consistentely fast changes.
Note: I was able to make the bit file changes to add 3 more encoder in expansion port.
This video was really helpful:
The encoder velocity has consistentely fast changes.
Note: I was able to make the bit file changes to add 3 more encoder in expansion port.
This video was really helpful:
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12067
- Thank you received: 4118
10 Jan 2025 22:36 #318669
by rodw
The THCAD 0 volt frequency should be what you observe on the encoder velocity pin give or take some bouncing around.
This offset needs to be entered in qtplasmac.
If you read the QTplasmac docs, there is a link to a calculator to determine your settings.
Replied by rodw on topic 7i96s Arc Voltage + Encoder Fault
Sounds like you have not correctly calibrated qtplasmac for your THCAD settingsWhen I turn on QTPlasmaC the value of Arc Voltage is 145.
The encoder velocity pin seems to be working fine on halshow.
The THCAD 0 volt frequency should be what you observe on the encoder velocity pin give or take some bouncing around.
This offset needs to be entered in qtplasmac.
If you read the QTplasmac docs, there is a link to a calculator to determine your settings.
The following user(s) said Thank You: sharp_reaper
Please Log in or Create an account to join the conversation.
- sharp_reaper
- Offline
- Senior Member
-
Less
More
- Posts: 73
- Thank you received: 7
16 Jan 2025 09:23 #319103
by sharp_reaper
SOS UPDATE:
Changed the THC to THCAD2 and change for a divided arc
Put the THCAD2 outside the plasma source in a plastic box.
Shielded only on THCAD2, in new cables.
Made the changes that you recommend:
Results:
This worked a week, but it happens again. The arc voltage is on -45.
I can take more pictures, make video. If anyone can help.
Replied by sharp_reaper on topic 7i96s Arc Voltage + Encoder Fault
I'm using the calculator from the PNCconf.If you read the QTplasmac docs, there is a link to a calculator to determine your settings.
SOS UPDATE:
Changed the THC to THCAD2 and change for a divided arc
Put the THCAD2 outside the plasma source in a plastic box.
Shielded only on THCAD2, in new cables.
Made the changes that you recommend:
Results:
This worked a week, but it happens again. The arc voltage is on -45.
I can take more pictures, make video. If anyone can help.
Attachments:
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12067
- Thank you received: 4118
16 Jan 2025 11:10 #319109
by rodw
Replied by rodw on topic 7i96s Arc Voltage + Encoder Fault
Now you have a THCAD 2 you can do more tests.
But normally, you would set the THCAD to use 1/32 frequency. This would alter your offsets etc accordingly. Make that change
Assuming a 10 volt range, apply a 9 volt battery to the THCAD HV input. The flashing light should change frequency. Does it?
the voltage should be about 90% of your full volt range. Is it?
What are the calibration frequencies for your THCAD on the sticker?
Read the encoder velocity at 0 volt at rest and at 9 volts.
What are these readings?
But normally, you would set the THCAD to use 1/32 frequency. This would alter your offsets etc accordingly. Make that change
Assuming a 10 volt range, apply a 9 volt battery to the THCAD HV input. The flashing light should change frequency. Does it?
the voltage should be about 90% of your full volt range. Is it?
What are the calibration frequencies for your THCAD on the sticker?
Read the encoder velocity at 0 volt at rest and at 9 volts.
What are these readings?
The following user(s) said Thank You: sharp_reaper
Please Log in or Create an account to join the conversation.
- sharp_reaper
- Offline
- Senior Member
-
Less
More
- Posts: 73
- Thank you received: 7
16 Jan 2025 14:22 #319125
by sharp_reaper
Replied by sharp_reaper on topic 7i96s Arc Voltage + Encoder Fault
Thank you Rod for your advice.
I'm testing when I have the chance. I can put the 1/32 divider frequency. I'm used to THCAD300 and always put on 1/128.
The sticker value for my THCAD2 is: FSV - 899.4 kHz | 0V - 96.8 kHz
The initial value for the offset was about 700 but I've noticed that when the Power Source is Down (No Power) the arc voltage is 0V. When I turn On the arc voltage goes to 12V.
Checked the encoder velocity pin with the value of 900. Put 900 in the offset. Arc voltage has 0V and got decent results.
Made some tests today. When I make the first pierce the arc voltage, in the first moments turn in -73 and then goes back to normal value.
After that the pierces (should be a higher value than the Cut Volts on material) seems normal to me.
Talked with the supplier of the plasma source and he refers HF equipment and to check the grounding. Reinforced the grounding connections which has a good grounding less than 0.3 Ohm.
I'm testing when I have the chance. I can put the 1/32 divider frequency. I'm used to THCAD300 and always put on 1/128.
The sticker value for my THCAD2 is: FSV - 899.4 kHz | 0V - 96.8 kHz
The initial value for the offset was about 700 but I've noticed that when the Power Source is Down (No Power) the arc voltage is 0V. When I turn On the arc voltage goes to 12V.
Checked the encoder velocity pin with the value of 900. Put 900 in the offset. Arc voltage has 0V and got decent results.
Made some tests today. When I make the first pierce the arc voltage, in the first moments turn in -73 and then goes back to normal value.
After that the pierces (should be a higher value than the Cut Volts on material) seems normal to me.
Talked with the supplier of the plasma source and he refers HF equipment and to check the grounding. Reinforced the grounding connections which has a good grounding less than 0.3 Ohm.