Setting Servo Max Acceleration
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18100
- Thank you received: 5326
25 Jan 2021 04:17 #196505
by PCW
Replied by PCW on topic Setting Servo Max Acceleration
The delay from LinuxCNCs commanded velocity output to analog out is in the 200 to 400 usec range with that hardware.
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 19898
- Thank you received: 4655
25 Jan 2021 09:19 #196510
by andypugh
Replied by andypugh on topic Setting Servo Max Acceleration
There is the potential for 1mS delay if the servo thread is set up to write-then-read.
But none of the config tools do that.
still, it might be worth looking at the thread order of components to be sure.
But none of the config tools do that.
still, it might be worth looking at the thread order of components to be sure.
Please Log in or Create an account to join the conversation.
- Michael
- Offline
- Platinum Member
-
Less
More
- Posts: 335
- Thank you received: 59
25 Jan 2021 17:19 #196538
by Michael
Replied by Michael on topic Setting Servo Max Acceleration
The analog output vs vel cmd seem to be fine and near instantaneous to me. That just leaves the wiring to the drive and the drive itself as sources of problems. 7i77 to drive wiring is only 2ft. I honestly think this delay is a source of tuning issues. As I get to a tune at higher and higher speeds my low speed tuning seems farther off. I can bring the f error spikes down to be consistent throughout the move at speed but going back to a lower speed introduces a under/overshoot that is worse then at high speed.
This is analog out vs vel cmd:
THis is the same tune with two different speeds, can't seem to find a middle ground.
P300 FF1 1.04 FF2 .0065 at 270 IPM
P300 FF1 1.04 FF2 .0065 at 60 IPM
This is analog out vs vel cmd:
THis is the same tune with two different speeds, can't seem to find a middle ground.
P300 FF1 1.04 FF2 .0065 at 270 IPM
P300 FF1 1.04 FF2 .0065 at 60 IPM
Attachments:
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 19898
- Thank you received: 4655
25 Jan 2021 18:23 #196544
by andypugh
This is not uncommon. I created the "lincurve" HAL component specifically for this purpose, so that the PID controller gains could be set up to vary with speed (or with temperature, error, etc)
In my day job I am in charge of tuning a system where P, I and D gains are each derived from a temperature / total error map, and there is a map for each of the 12 gears.
Replied by andypugh on topic Setting Servo Max Acceleration
As I get to a tune at higher and higher speeds my low speed tuning seems farther off.
This is not uncommon. I created the "lincurve" HAL component specifically for this purpose, so that the PID controller gains could be set up to vary with speed (or with temperature, error, etc)
In my day job I am in charge of tuning a system where P, I and D gains are each derived from a temperature / total error map, and there is a map for each of the 12 gears.
Please Log in or Create an account to join the conversation.
- Michael
- Offline
- Platinum Member
-
Less
More
- Posts: 335
- Thank you received: 59
25 Jan 2021 21:35 #196563
by Michael
Replied by Michael on topic Setting Servo Max Acceleration
I would have no problem going that route but would like for one of the two issues (delayed response, over current at speed) I have to be solved before I go any further with these motors.
Some other thoughts that come to mind. The issue could be a delay in the drive sending out an encoder count. From what I read a lot of these servo's are not a direct pass through on the encoder. The delayed encoder counts would create a similar response. I don't have to use the drives encoder to Linuxcnc, I could use a glass or magnetic scale on each axis, would have a few extra benefits as well. Just some thoughts, I think by the time I added those in I would be near the cost of more name brand servo products, which is another option.
Some other thoughts that come to mind. The issue could be a delay in the drive sending out an encoder count. From what I read a lot of these servo's are not a direct pass through on the encoder. The delayed encoder counts would create a similar response. I don't have to use the drives encoder to Linuxcnc, I could use a glass or magnetic scale on each axis, would have a few extra benefits as well. Just some thoughts, I think by the time I added those in I would be near the cost of more name brand servo products, which is another option.
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21959
- Thank you received: 7478
25 Jan 2021 21:45 #196565
by tommylight
Replied by tommylight on topic Setting Servo Max Acceleration
Screenshots look much better now.
Please Log in or Create an account to join the conversation.
- Michael
- Offline
- Platinum Member
-
Less
More
- Posts: 335
- Thank you received: 59
27 Jan 2021 21:17 #196816
by Michael
Replied by Michael on topic Setting Servo Max Acceleration
So continuing to beat this dead horse. I was able to get the DMM servo/drive combo to reach full speed in its RS232 internal position mode. It was able to accelerate to speed at .18 seconds time consistently. So taking this information back to Linuxcnc analog settings and taking 10% (45ips/s) off to allow for room to maneuver I was still unable to go over 2/3 speed without an over current fault. In fact I wasn't able to get up to speed at half that (20ips/s) acceleration without over current. Double checking the drives current monitor vs the halscope shows that the delayed response is causing an increased velocity command to get the motor up to acceleration parameters, accelerating faster than it can handle.
So taking all this information back to DMM technical help and they responded that the problem is on the Mesa side and that I need to work with mesa to figure it out. Obviously I don't think that is accurate. They also stated to use an oscilloscope to confirm the delay since there stated response time is 300 usec. Unfortunately I don't have one of those and also never used one but could probably figure it out. Any advice on finding/acquiring an oscilloscope to get the information and send it back to DMM? At this point I would very much like to see exactly what the problem is.
Any way to definitively rule out the computer and FPGA as being a problem, past what we have already done? Kind of fell like I bought a car that should do 60 mph but can only get up to 40. Yeah I can get it to work but its not what I paid for from DMM.
So taking all this information back to DMM technical help and they responded that the problem is on the Mesa side and that I need to work with mesa to figure it out. Obviously I don't think that is accurate. They also stated to use an oscilloscope to confirm the delay since there stated response time is 300 usec. Unfortunately I don't have one of those and also never used one but could probably figure it out. Any advice on finding/acquiring an oscilloscope to get the information and send it back to DMM? At this point I would very much like to see exactly what the problem is.
Any way to definitively rule out the computer and FPGA as being a problem, past what we have already done? Kind of fell like I bought a car that should do 60 mph but can only get up to 40. Yeah I can get it to work but its not what I paid for from DMM.
Please Log in or Create an account to join the conversation.
- Todd Zuercher
-
- Offline
- Platinum Member
-
Less
More
- Posts: 4786
- Thank you received: 1476
27 Jan 2021 21:30 #196824
by Todd Zuercher
Replied by Todd Zuercher on topic Setting Servo Max Acceleration
Which DMM amps do you have? I've gotten the impression most of their product is geared towards step/dir input, and analog is kind of an afterthought.
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 19898
- Thank you received: 4655
27 Jan 2021 21:38 #196827
by andypugh
You might be able to dial the current back by limiting the PID.
There are a number of parameters that could help.
pid.N.maxoutput float in
Output limit. The absolute value of the output will not be permitted to exceed maxoutput, unless maxoutput is zero. When the output is limited, the error integrator will hold instead of integrating, to prevent windup and overshoot.
pid.N.maxerror float in
Limit on the internal error variable used for P, I, and D. Can be used to prevent high Pgain values from generating large outputs under conditions when the error is large (for example, when the command makes a step change). Not normally needed, but can be useful when tuning non-linear systems.
pid.N.maxerrorD float in
Limit on the error derivative. The rate of change of error used by the Dgain term will be limited to this value, unless the value is zero. Can be used to limit the effect of Dgain and prevent large output spikes due to steps on the command and/or feedback. Not normally needed.
pid.N.maxerrorI float in
Limit on error integrator. The error integrator used by the Igain term will be limited to this value, unless it is zero. Can be used to prevent integrator windup and the resulting overshoot during/after sustained errors. Not normally needed.
pid.N.maxcmdD float in
Limit on command derivative. The command derivative used by FF1 will be limited to this value, unless the value is zero. Can be used to prevent FF1 from producing large output spikes if there is a step change on the command. Not normally needed.
pid.N.maxcmdDD float in
Limit on command second derivative. The command second derivative used by FF2 will be limited to this value, unless the value is zero. Can be used to prevent FF2 from producing large output spikes if there is a step change on the command. Not normally needed.
pid.N.maxcmdDDD float in
Limit on command third derivative. The command third derivative used by FF3 will be limited to this value, unless the value is zero. Can be used to prevent FF3 from producing large output spikes if there is a step change on the command. Not normally needed.
Replied by andypugh on topic Setting Servo Max Acceleration
Double checking the drives current monitor vs the halscope shows that the delayed response is causing an increased velocity command to get the motor up to acceleration parameters, accelerating faster than it can handle.
You might be able to dial the current back by limiting the PID.
There are a number of parameters that could help.
pid.N.maxoutput float in
Output limit. The absolute value of the output will not be permitted to exceed maxoutput, unless maxoutput is zero. When the output is limited, the error integrator will hold instead of integrating, to prevent windup and overshoot.
pid.N.maxerror float in
Limit on the internal error variable used for P, I, and D. Can be used to prevent high Pgain values from generating large outputs under conditions when the error is large (for example, when the command makes a step change). Not normally needed, but can be useful when tuning non-linear systems.
pid.N.maxerrorD float in
Limit on the error derivative. The rate of change of error used by the Dgain term will be limited to this value, unless the value is zero. Can be used to limit the effect of Dgain and prevent large output spikes due to steps on the command and/or feedback. Not normally needed.
pid.N.maxerrorI float in
Limit on error integrator. The error integrator used by the Igain term will be limited to this value, unless it is zero. Can be used to prevent integrator windup and the resulting overshoot during/after sustained errors. Not normally needed.
pid.N.maxcmdD float in
Limit on command derivative. The command derivative used by FF1 will be limited to this value, unless the value is zero. Can be used to prevent FF1 from producing large output spikes if there is a step change on the command. Not normally needed.
pid.N.maxcmdDD float in
Limit on command second derivative. The command second derivative used by FF2 will be limited to this value, unless the value is zero. Can be used to prevent FF2 from producing large output spikes if there is a step change on the command. Not normally needed.
pid.N.maxcmdDDD float in
Limit on command third derivative. The command third derivative used by FF3 will be limited to this value, unless the value is zero. Can be used to prevent FF3 from producing large output spikes if there is a step change on the command. Not normally needed.
Please Log in or Create an account to join the conversation.
- Michael
- Offline
- Platinum Member
-
Less
More
- Posts: 335
- Thank you received: 59
27 Jan 2021 22:40 - 28 Jan 2021 17:01 #196836
by Michael
My post purchase research indicates the same. I wasn't able to find any successful examples of DMM servos in analog speed mode.
I have the DYN4-T01A2-00 Servo Drive. I am just about to buy a 7i78 and cable. The downside is I will lose index homing until 2.9 is ready and even trying to close the position with step and direction maybe problematic if the encoder is delayed in responding. I can keep it velocity but run 2/3 speed which isnt bad but I am also concerned the continual current spikes won't do well for drive/motor longevity.
Replied by Michael on topic Setting Servo Max Acceleration
Which DMM amps do you have? I've gotten the impression most of their product is geared towards step/dir input, and analog is kind of an afterthought.
My post purchase research indicates the same. I wasn't able to find any successful examples of DMM servos in analog speed mode.
I have the DYN4-T01A2-00 Servo Drive. I am just about to buy a 7i78 and cable. The downside is I will lose index homing until 2.9 is ready and even trying to close the position with step and direction maybe problematic if the encoder is delayed in responding. I can keep it velocity but run 2/3 speed which isnt bad but I am also concerned the continual current spikes won't do well for drive/motor longevity.
Last edit: 28 Jan 2021 17:01 by Michael.
Please Log in or Create an account to join the conversation.