5 years 7 months ago #201536 by andypugh
If you have 3-phase and you are keeping the variator then you have no reason to run the spindle motor from a VFD.

Please Log in or Create an account to join the conversation.

More
5 years 7 months ago - 5 years 7 months ago #201537 by RotarySMP
Space.
I removed the enormous electrical cabinet, and need to shoe horn everything into the pneumatic bay. 5 contactors and their wiring take up more space than one contactor and a VFD.

Also those existing contactors need 48VAC for their coils. I am pulling the huge Transformer, so replacing all of them is dearer than a VFD.
Last edit: 5 years 7 months ago by RotarySMP.

Please Log in or Create an account to join the conversation.

More
5 years 7 months ago - 5 years 7 months ago #201539 by Aciera
Replied by Aciera on topic Schaublin 125-CNC retrofit.

Does insulation failure and shorting cause a fire risk outside the motor, or just a stinky dead motor?


I my case it just ended with an insulation break down to the metal body (ie. phase-earth fault) so the circuit braker got activated. If you have your motor properly grounded and your electrical installation is in order I don't see a terribly increased risk. Although having said that, I once witnessed the windings of a rather small 3kW motor go up in smoke in a sawmill. The amount of smoke coming out of that thing was unreal. Even after cutting all power to it it continued to smoke for what felt like a very long time. There was no VFD involved though.

So what did I learn from this?
If I do work for somebody else I refuse to hook up a VFD to a motor that is not isol class F but if it's my shop I might try.
Not sure if this helps you in any way though.:unsure:

[edit]
Really considering that you have a way to automate the variator I don't see why you would need a VFD. I'm not sure a VFD will actually save all that much space if you modernize the contactors but I might be wrong.

[edit2]

I wonder if it is relevant that I have the motor cables running through a common-mode chole at the VFD outlet?

maybe, but really I have no idea. To be honest, I didn't bother much with insulation classification before that motor on my mill failed. Just like I used to think electromagnetic shielding was mostly a nice to have but not relevant in my life. That one really hit me on the head one day and I shield everything now. :whistle:
Last edit: 5 years 7 months ago by Aciera.

Please Log in or Create an account to join the conversation.

More
5 years 7 months ago #201544 by anfänger
Short question to the VFD. Would it be OK to use the VFD as a soft statt or should it start at 40hz right away?

Please Log in or Create an account to join the conversation.

More
5 years 7 months ago - 5 years 7 months ago #201551 by PCW
Replied by PCW on topic Schaublin 125-CNC retrofit.

andypugh wrote:

Aciera wrote: I know there are people out there who have been running motors with isolation class B on VFD's for years. I guess what I'm trying to say is that using a VFD on motors with isolation class lower than F can indeed destroy the motor. So really it comes down to how badly it's going to hurt to replace that motor.
.


I wonder if it is relevant that I have the motor cables running through a common-mode chole at the VFD outlet?



It probably helps a bit by reducing the phase--> ground high frequency currents
that cause insulation heating. A real load inductor on the VFD outputs would help a
lot more (by greatly reducing the high frequency components in the VFD output)

This kind of device:

www.automationdirect.com/adc/shopping/ca...ine_reactors/lr-4015
Last edit: 5 years 7 months ago by PCW.
The following user(s) said Thank You: J Green

Please Log in or Create an account to join the conversation.

More
5 years 7 months ago #201558 by andypugh

RotarySMP wrote: Space.
I removed the enormous electrical cabinet, and need to shoe horn everything into the pneumatic bay. 5 contactors and their wiring take up more space than one contactor and a VFD.
Also those existing contactors need 48VAC for their coils. I am pulling the huge Transformer, so replacing all of them is dearer than a VFD.


How about using SSRs controlled by HAL logic?
www.amazon.de/-/en/X-DREE-3-32VDC-semico...16efccb9d559b528ebea
Easily triggered by GPIO, so no 48VAC needed. You would need one for each direction of the Dahlander, I assume. I would probably keep one big clunky contactor as the master power breaker.
The following user(s) said Thank You: RotarySMP