7i97t with 7i84d connection problem
2 years 2 months ago - 2 years 2 months ago #307475 by PCW
Yes. the sample hal file uses a 192.168.1.121 IP address:
loadrt hm2_eth board_ip="192.168.1.121" config=" num_encoders=6 num_pwmgens=6 num_stepgens=0 sserial_port_0=00xxxxxx"
The 7I84D is not recognized.
This may be because:
1. The Ethernet cable is not EIA 568B, so the color code is
not correct for the chart in the manual
(check the RJ45 end of the cable)
2. You don't have _both_ VFIELDA and VFIELDB connected to +8 to +24V
on the 7I84
Last edit: 2 years 2 months ago by PCW.
The following user(s) said Thank You: Krulli_Fräser
2 years 2 months ago #307476 by Krulli_Fräser
Thanks for your input.
my rj 45 plug looks like this
I have the 7i84 connected to 24V
on the left the calbe marked 55 is 24V an i jumpered it over so both field connectors get 24v
the cable marked 53 is ground. There are no relays or switches between the power supply and 7i84 as per the manual.
I have the 7i97 connected to 5V
The violet cable supplies 5V, the blue one is ground.
The 7i97 seems to work, as I am able to read the handwheel encoders I have connected.
After changing the ip to 10.10.10.10 LCNC starts with Peter's hal file, but the 7i84 still doesn't show up in halshow
2 years 2 months ago #307477 by Krulli_Fräser
Update:
I also have a 7i73 which will later be mounted in the control unit to interface some buttons and encoders, and plugging the cat5 cable from the 7i84 to it and running mesaflash --addr 10.10.10.10 --device=ETHER --sserial
gives this:
SSLBP port 0:   SSLBP Version: 1.43   SSLBP Channels: 1   SSLBP Baud Rate: 2500000   sserial device at channel 0: 7I73 (unit 0x130002FC)     SwRevision = 14     HwRevision = 1     NVBaudRate = 2.5Mb     NVUnitNumber = 0x130002FC     NVWatchDogTimeout = 50ms     SOFTWARE MODE InputOutputEncoder [index 00]     SOFTWARE MODE InputOutputEncoderAnalog [index 01]     SOFTWARE MODE InputOutputEncoderAnalog [index 02]     SOFTWARE MODE InputOutputEncoderDisplay [index 00]     SOFTWARE MODE InputOutputEncoderAnalogDisplay [index 01]     SOFTWARE MODE InputOutputEncoderAnalogWideDisplay [index 02]     SOFTWARE MODE InputOutputEncoderKeycode4by8 [index 00]     SOFTWARE MODE InputOutputEncoderAnalogKeycode4by8 [index 01]     SOFTWARE MODE InputOutputEncoderAnalogKeycode4by8 [index 02]     SOFTWARE MODE InputOutputEncoderDisplayKeycode4by8 [index 00]     SOFTWARE MODE InputOutputEncoderAnalogDisplayKeyCode4by8 [index 01]     SOFTWARE MODE InputOutputEncoderAnalogWideDisplayKeyCode4by8 [index 02]     SOFTWARE MODE InputOutputEncoderKeycode8by8 [index 00]     SOFTWARE MODE InputOutputEncoderAnalogKeyCode8by8 [index 01]     SOFTWARE MODE InputOutputEncoderAnalogKeyCode8by8 [index 02]     SOFTWARE MODE InputOutputEncoderDisplayKeycode8by8 [index 00]     SOFTWARE MODE InputOutputEncoderAnalogDisplayKeyCode8by8 [index 01]     SOFTWARE MODE InputOutputEncoderAnalogWideDisplayKeyCode8by8 [index 02]
which leads me to believe that card is communicating properly
Thanks for your help so far
2 years 2 months ago #307478 by PCW
It looks like the 7I84D has failed somehow.
There is either an issue with the 3.3V supply
or the microcontroller, because neither the
red fault or green activity LED is illuminated.
2 years 2 months ago #307479 by Krulli_Fräser
Is that something I can check/fix myself or should I contact the retailer. The package arrived on friday and I am fairly certain I didn't damage it.
2 years 2 months ago - 2 years 2 months ago #307481 by PCW
You could check if there is 3.3V power, and if not, maybe trace
backwards (3.3V comes from a switching supply that is supplied
by VFIELDB)
 (Check across the larger electrolytic capacitor
 C30 towards the bottom of the card between TB2 and TB3)
But if its not something obvious, the card should be returned
to the vendor for repair/replacement.
Moderators: PCW, jmelson
Time to create page: 0.327 seconds