Replied by andypugh on topic Convert from Anilam Crusader M to EMC 2

Ok. Does the 7i33 have that option as well?

Not as far as I know.

or am I better off using a 3rd board dedicated to A/D for a high resolution conversion? It would work better, I think. The 7i87 is 12-bit and can plug into a 7i77. That gives you 8 +/- 10V inputs which sounds fairly well suited for reading tachometer inputs. That would measure as little as 2.4mV up to 10V, whereas the ones on the 7i77 board are 8-bits and so read from 13mV to 3.3V (and possibly not very well)

If the tachos are 3V / 1000rpm then the 7i87 will measure 0.8rpm to 3300rpm, whereas the 7i77 built-in Analogue will only be good for 4.3 rpm to 1100rpm.

Take advice from Pete / Mesa before buying though.

Please Log in or Create an account to join the conversation.

More
10 Jan 2013 08:11 #28531 by andypugh
Replied by andypugh on topic Convert from Anilam Crusader M to EMC 2

Ok. Does the 7i33 have that option as well?

Not as far as I know.

or am I better off using a 3rd board dedicated to A/D for a high resolution conversion

? It would work better, I think. The 7i87 is 12-bit and can plug into a 7i77. That gives you 8 +/- 10V inputs which sounds fairly well suited for reading tachometer inputs. That would measure as little as 2.4mV up to 10V, whereas the ones on the 7i77 board are 8-bits and so read from 13mV to 3.3V (and possibly not very well)

If the tachos are 3V / 1000rpm then the 7i87 will measure 0.8rpm to 3300rpm, whereas the 7i77 built-in Analogue will only be good for 4.3 rpm to 1100rpm.

Take advice from Pete / Mesa before buying though.

Please Log in or Create an account to join the conversation.

More
10 Jan 2013 23:02 - 17 Feb 2013 03:15 #28550 by ryankracht
Replied by ryankracht on topic Convert from Anilam Crusader M to EMC 2
Next, I plan to confirm that all limit switches are still present in the circuit, and test the x and y axis as well. Finally, I plan to generate a reference signal and attempt to move all axis.

My goal during this upgrade will be to use all existing hardware. It appears that no-one has successfully done this, but I don't know why this shouldn't be possible. Anilam had a functional control after all. From reading other posts, my understanding is that drives get a tach feedback, and the motion controller gets (relatively low resolution) position feedback from "glass scales". I know of one successful Anilam to EMC via PPMC, although he had to add rotary encoders. I would like to avoid this, or at least understand why my current set-up won't work.

I am open to various motion control options at this point, my preference would go to whatever can drive my current hardware most efficiently for a reasonable cost.

Update on Progress:

- Confirmed function of all limit switches (single switch per axis--activated by dual fixed cams...one on each end of travel of the axis)...Done. E-stop will not reset if limit switch is tripped, system will e-stop if limit is reached while running.

- There is a spare terminal (P8) on the Anilam PCB 803 (see pic). If you bring pin 13 to gnd (pin14), the servos will enable upon e-stop reset. I wired in a momentary switch to this terminal so that I could keep my finger on a "deadman switch" while testing.

- Confirmed power up of all drives...done. There is no drift to the z axis, but some small very slow drift to the x and y.

- wired a 9V battery (see pic) to provide a 0 to ~3 V signal into the drives. To do this, I used pins 1-6 of the same terminal (P8) of PCB 803. I also needed to pull the connector from the Anilam control board that was outputting voltage. (PCB 502) Confirmed that I can drive both directions and stop. Done. Interesting that I can get rid of the small drift on x and y by applying a small control voltage. (seems like a good sign). I confirmed that positive voltage to the red wires give positive axis movement (from tool reference)

- checked tachs by measuring voltage across wires. I was surprised that this worked with the power off. I attempted to crank the axis as fast as I could, but I imagine that this is not as fast as they used to move when the controller worked. I measured about 5V max on the x and y, but saw up to 10V on the Z. The Z appears to have much more reduction, so I believe I could get the motor spinning faster with the mechanical advantage that I could use on that axiz. I am concerned that a 0-10V analog input is not a large enough range. I would not be surprised if the tach's output 0-15V like the signal input to the drives. If no 0-15V input is available, I will likely have to step down the voltage to make use of what is available. There is no convienent way to get this signal out as the tach's go directly into the drive. I needed to stick probe wires into the back of the connector to measure. TODO: confirm that the drive wasn't affecting this signal, unplug the connector and test again.

- I was surprised to see that with the axis moving in a positive direction (from tool reference) the tach sent a negative voltage.
Attachments:
Last edit: 17 Feb 2013 03:15 by ryankracht.

Please Log in or Create an account to join the conversation.

More
10 Jan 2013 23:47 #28551 by andypugh
Replied by andypugh on topic Convert from Anilam Crusader M to EMC 2

- checked tachs by measuring voltage across wires. I was surprised that this worked with the power off. I attempted to crank the axis as fast as I could, but I imagine that this is not as fast as they used to move when the controller worked. I measured about 5V max on the x and y, but saw up to 10V on the Z. The Z appears to have much more reduction, so I believe I could get the motor spinning faster with the mechanical advantage that I could use on that axiz. I am concerned that a 0-10V analog input is not a large enough range. I would not be surprised if the tach's output 0-15V like the signal input to the drives. If no 0-15V input is available, I will likely have to step down the voltage to make use of what is available.

You probably need bipolar reading A to D to sense the two directions. the 7i87 is safe to 100V so it might well not matter if the speed input tops-out during fast moves. The suggestion to use the tachs is purely to aid tuning at very slow movement rates.
Normally the PID loop calculates its rate of change by differentiating encoder position counts, which for a relatively coarse feedback system like your glass scale may be rather noisy.
Wiring the tach signals to the pid.N.feedback-deriv pins gives the PID controller a much less noisy and more accurate velocity input.
Note that the inut to this pin is only used for the D-term of the PID, so you will not see any benefit from it with no Dgain.
Whether $99 for the 7i87 is worth the investment is a choice you need to make, but I think it should really help to reduce dither between scale counts.
Other conversions have tended to add encoders to the motors, but this is probably even more expensive.
I think that the encoder conversion bases P and D on the motor encoder and I on the scales.
The proposal here would be to base P and I on the scales and D on the tach/7i87.
But I am aware that I am performing a thought experiment with your money here.

I was surprised to see that with the axis moving in a positive direction (from tool reference) the tach sent a negative voltage.

This is a non-issue and can be solved in HAL.
It is probably deliberate, the driver scheme is probably very simple, where the command voltage and tach voltage are summed, amplified and sent direct to the motors.

Please Log in or Create an account to join the conversation.

More
11 Jan 2013 00:02 - 11 Jan 2013 00:16 #28552 by PCW
Replied by PCW on topic Convert from Anilam Crusader M to EMC 2
Even with ability to read the tachometer,you are still 'dead reckoning' between scale counts and with enough idle time you will drift until you hit a scale count. So when idle I suspect all you will accomplish is to lower the frequency of the +-1 count dither that you normally get with digital encoder feedback systems. It should work well when moving if implemented correctly though.

As Andy mentioned, a negative tachometer reading in a positive direction is expected since the tachometer is negative feedback
(the negative tachometer output is summed with the positive command voltage when moving in a positive direction)

Its easy to extend the 7I87 input range (adding a 100K input resistor will increase the range to +-20V)
Last edit: 11 Jan 2013 00:16 by PCW.

Please Log in or Create an account to join the conversation.

More
11 Jan 2013 00:29 #28553 by andypugh
Replied by andypugh on topic Convert from Anilam Crusader M to EMC 2

Even with ability to read the tachometer,you are still 'dead reckoning' between scale counts and with enough idle time you will drift until you hit a scale count

I wonder if you could integrate tacho data and add it to the position, rather like the "position interpolated" in the software encoder?

With some D-term shouldn't the drift be spotted and nulled?

Please Log in or Create an account to join the conversation.

More
11 Jan 2013 00:36 - 11 Jan 2013 00:44 #28554 by PCW
Replied by PCW on topic Convert from Anilam Crusader M to EMC 2
Sure thats what dead reckoning is, but there will always be accumulative errors so the position will drift when idle.

It may actually be that you dont care about the tachometer voltage above a volt or so, since you can use encoder velocity signals for interpolation when moving at any reasonable rate.
So maybe a +- 1V full scale range might be better (with some input clamping method)

All in all I wonder if adding a high resolution rotary encoder to the ballscrew end is not going to be better ultimate solution
Last edit: 11 Jan 2013 00:44 by PCW. Reason: additions

Please Log in or Create an account to join the conversation.

More
11 Jan 2013 00:44 #28555 by andypugh
Replied by andypugh on topic Convert from Anilam Crusader M to EMC 2
Previous attempts at this conversion have suggested that there is a problem with the loose coupling of the machine position to the motors, and the relatively high granularity of the position feedback.

In practice 10um error in absolute machine position is pretty reasonable for a milling machine as long as it can avoid dithering between counts.
The tacho feedback ought to be able to help with the loose coupling problem, even if we don't know exactly how yet.

It might actually be a good plan to run two PID loops, a velocity loop controlling the motors with tachos as feedback, then a position loop using the scales as feedback and making velocity requests.

Please Log in or Create an account to join the conversation.

  • Todd Zuercher
  • Todd Zuercher's Avatar
  • Online
  • Platinum Member
  • Platinum Member
More
11 Jan 2013 05:40 #28562 by Todd Zuercher
Replied by Todd Zuercher on topic Convert from Anilam Crusader M to EMC 2
I have to wonder how the original hardware handled it. Did the tack signal go to just the drive or the drive and control? If it only went to the drive, and the drive is handling the velocity loop, then might the corser scale feed back to the control be enough?

Just the ponderings of a person who doesn't realy know what they are talking about.

Please Log in or Create an account to join the conversation.

More
12 Jan 2013 07:43 #28612 by spangledboy
Replied by spangledboy on topic Convert from Anilam Crusader M to EMC 2
I'm going through almost exactly the same upgrade path myself - 0.01mm resolution linear scales, Anilam crusader II control, analogue drives with tach feedback.

I can confirm that on my Crusader control the tach feedback only went to the drives. The encoders connected straight back to one of the Crusader boards while the analogue control signals came from a different board to the drives.

On careful inspection of the wiring schematic and detailed testing of what pin went where I managed to deduce that the majority of the pins on the massive round multi pin plug did nothing at all. One impressive looking 26 conductor ribbon cable in the control box turned out to only actually have 5 wires doing anything at all.