- Posts: 243
- Thank you received: 62
Please Log in or Create an account to join the conversation.
Thanks for your speculations. That kinda makes sense.So addressing your questions:
1. Because each individual conductor should stay below the individual conductor max temp of 105c when the cable is operated at xxx amps at yyy temp. To see if this is the case, look up other cables in the same Belden family and compare the 2-conductor to a 12 (or more) conductor of the same AWG. I bet the high-conductor count cable has a lower amp-per-conductor rating than the 2-wire.
2. Because they're different cables, meeting different specifications and intended for different use-cases.
3. I would treat the number given is their max rating, but you should contact Belden for clarification.
Please Log in or Create an account to join the conversation.
Thanks. I was not aware of this classification. I will look into it.Use MTW for current carrying applications.
MTW Wire - UL 1015
A type of hookup wire with a highly stranded bare copper conductor typically used in control cabinets, machine tool applications, and appliance wiring applications such as HVAC equipment. Wire & Cable Applications for MTW Wires are best for use in dry locations at 90°C, or not to exceed 60°C in wet locations or where exposed to oils or coolants.
The Beldon cable is best for signal applications. It is a bit of overkill for most switch inputs.
Please Log in or Create an account to join the conversation.
Please Log in or Create an account to join the conversation.
Please Log in or Create an account to join the conversation.
Please Log in or Create an account to join the conversation.