Analog servo drive enable
- PCW
-
- Away
- Moderator
-
Less
More
- Posts: 18084
- Thank you received: 5317
19 Mar 2021 17:12 #202861
by PCW
Replied by PCW on topic Analog servo drive enable
A fast short movement when first enabled suggest the the feedback is
backwards (the fix is to change the sign of OUTPUT_SCALE)
backwards (the fix is to change the sign of OUTPUT_SCALE)
Please Log in or Create an account to join the conversation.
- Hamel2020
-
Topic Author
- Offline
- Senior Member
-
Less
More
- Posts: 74
- Thank you received: 2
19 Mar 2021 17:45 #202865
by Hamel2020
Replied by Hamel2020 on topic Analog servo drive enable
Actually I changed the OUTPUT_SCALE signal , but not difference ...
Peter ... Yesterday you told me may be the loop is not closed ... [ How can I verify that ] ??
- The Encoder feedback is ok as per the screen shoot i attached
- The drive enable also working properly .
So anything else I have to check it , to stop the slow rotation of the motor before enable ... ?
Peter ... Yesterday you told me may be the loop is not closed ... [ How can I verify that ] ??
- The Encoder feedback is ok as per the screen shoot i attached
- The drive enable also working properly .
So anything else I have to check it , to stop the slow rotation of the motor before enable ... ?
Please Log in or Create an account to join the conversation.
- PCW
-
- Away
- Moderator
-
Less
More
- Posts: 18084
- Thank you received: 5317
19 Mar 2021 17:53 - 19 Mar 2021 17:54 #202866
by PCW
Replied by PCW on topic Analog servo drive enable
Is the behaviour different with OUTPUT_SCALE reversed?
What are your P,I,D settings?
The drive should not drift if not enabled It sounds like either the drive is still enabled
(check with a voltmeter on the drive enable input) or the drive is not programmed to obey the enable input
What are your P,I,D settings?
The drive should not drift if not enabled It sounds like either the drive is still enabled
(check with a voltmeter on the drive enable input) or the drive is not programmed to obey the enable input
Last edit: 19 Mar 2021 17:54 by PCW.
Please Log in or Create an account to join the conversation.
- Hamel2020
-
Topic Author
- Offline
- Senior Member
-
Less
More
- Posts: 74
- Thank you received: 2
19 Mar 2021 18:49 #202876
by Hamel2020
Replied by Hamel2020 on topic Analog servo drive enable
- No reversed ? remain same direction .
- the PID i'm using : P= 50 I= 0 D = 0 (attached img)
======================================
As per the sketch I used the circuit breaker as switch .
So when : switch on => driver enabled
when : switch off => driver disable
Suppose to be the write wiring … but not right control because where is the effect of the net :
net x-enable <= joint.0.amp-enable-out
net x-enable => hm2_7i76e.0.7i77.0.3.analogena
when I measure between [ ENOA- & 0V ] I got +24V reading
and when I measure between [ ENOA+ & 0V ] also I got +24V reading
while I did not press the enable from the axis gui ?
that means I got +24 from both ENOA- & ENOA+
==================================
- the PID i'm using : P= 50 I= 0 D = 0 (attached img)
======================================
As per the sketch I used the circuit breaker as switch .
So when : switch on => driver enabled
when : switch off => driver disable
Suppose to be the write wiring … but not right control because where is the effect of the net :
net x-enable <= joint.0.amp-enable-out
net x-enable => hm2_7i76e.0.7i77.0.3.analogena
when I measure between [ ENOA- & 0V ] I got +24V reading
and when I measure between [ ENOA+ & 0V ] also I got +24V reading
while I did not press the enable from the axis gui ?
that means I got +24 from both ENOA- & ENOA+
==================================
Please Log in or Create an account to join the conversation.
- PCW
-
- Away
- Moderator
-
Less
More
- Posts: 18084
- Thank you received: 5317
19 Mar 2021 19:01 - 19 Mar 2021 19:03 #202880
by PCW
Replied by PCW on topic Analog servo drive enable
ENA0+ should be 24V (since its connected to +24V)
if ENA0- is at 24V when linuxCNC is not running then you
either have a wiring error or the ENA output has been damaged
somehow.
What does the drives enable pin read when unconnected?
Does the drive drift if the circuit breaker is off?
if ENA0- is at 24V when linuxCNC is not running then you
either have a wiring error or the ENA output has been damaged
somehow.
What does the drives enable pin read when unconnected?
Does the drive drift if the circuit breaker is off?
Last edit: 19 Mar 2021 19:03 by PCW.
Please Log in or Create an account to join the conversation.
- Hamel2020
-
Topic Author
- Offline
- Senior Member
-
Less
More
- Posts: 74
- Thank you received: 2
19 Mar 2021 19:14 #202882
by Hamel2020
Replied by Hamel2020 on topic Analog servo drive enable
I check it even the linuxcnc is not running , still ENA0 give me 24v .
When I off the breaker , the driver shown indication shows the driver not enabled .
When the breaker is off ,,, the motor is not drifting .
When I off the breaker , the driver shown indication shows the driver not enabled .
When the breaker is off ,,, the motor is not drifting .
Please Log in or Create an account to join the conversation.
- PCW
-
- Away
- Moderator
-
Less
More
- Posts: 18084
- Thank you received: 5317
19 Mar 2021 19:38 - 19 Mar 2021 19:44 #202885
by PCW
Replied by PCW on topic Analog servo drive enable
if ENA0+ to ENA0- (disconnected from all external circuits)
Reads as anything other than an open circuit with a DVM
(on Ohms range and Meter+ to ENA0+, Meter- to ENA0-)
it is broken. You might try another ENA channel with this
test (ENA0 through ENA4 are all controlled by analogena)
Reads as anything other than an open circuit with a DVM
(on Ohms range and Meter+ to ENA0+, Meter- to ENA0-)
it is broken. You might try another ENA channel with this
test (ENA0 through ENA4 are all controlled by analogena)
Last edit: 19 Mar 2021 19:44 by PCW.
Please Log in or Create an account to join the conversation.
- Hamel2020
-
Topic Author
- Offline
- Senior Member
-
Less
More
- Posts: 74
- Thank you received: 2
19 Mar 2021 23:22 #202910
by Hamel2020
Replied by Hamel2020 on topic Analog servo drive enable
Peter .... I really appreciate your help ...
I found the fault of the Enable , it was wiring DB25 mistake
So the enable issue .. sorted .
I follow your comments previously said to a member in the forum ..
forum.linuxcnc.org/38-general-linuxcnc-q...nt-0-following-error
I followed the exact steps .... Once I enable the driver (from linuxcnc) the motor start spinning shortly and then get joint following error
P Range [10 - 50 ] , I : 0, D : 0
FERROR : 15, MIN_FERROR : 15
I found the fault of the Enable , it was wiring DB25 mistake
So the enable issue .. sorted .
I follow your comments previously said to a member in the forum ..
forum.linuxcnc.org/38-general-linuxcnc-q...nt-0-following-error
I followed the exact steps .... Once I enable the driver (from linuxcnc) the motor start spinning shortly and then get joint following error
P Range [10 - 50 ] , I : 0, D : 0
FERROR : 15, MIN_FERROR : 15
Please Log in or Create an account to join the conversation.
- PCW
-
- Away
- Moderator
-
Less
More
- Posts: 18084
- Thank you received: 5317
20 Mar 2021 00:16 #202917
by PCW
Replied by PCW on topic Analog servo drive enable
Running away like that points to reversed feedback
Does it runaway with P = 0?
Does it runaway with P = 0?
Please Log in or Create an account to join the conversation.
- Hamel2020
-
Topic Author
- Offline
- Senior Member
-
Less
More
- Posts: 74
- Thank you received: 2
20 Mar 2021 01:32 #202923
by Hamel2020
Replied by Hamel2020 on topic Analog servo drive enable
I have one more question ...
How is the analog signaling from 7i77 at drives [0-5] (AUT0 , GND)
is it differential? or single ended ?
ie :
AUT0 => -10 to +10 V
GND => 0 V
or
AUT0 => +10 V
GND => -10 V
How is the analog signaling from 7i77 at drives [0-5] (AUT0 , GND)
is it differential? or single ended ?
ie :
AUT0 => -10 to +10 V
GND => 0 V
or
AUT0 => +10 V
GND => -10 V
Please Log in or Create an account to join the conversation.
Time to create page: 0.198 seconds