Ive got the 7i96s input connected to the PSU +24v (i redid all the limits etc) but the DCM terminal of VFD is connected to the Out0- pin (for the enable function). Is it ok to have both the Out0- and the 7i96s isolated input connected to DCM on the VFD? I dont see any other way for it to get both. I actually need to do two additional inputs.
Replied by supermoto on topic Logic assignments for VFD/Spindle control and EStops (7i96s)
Yes. the UPF and DRV outputs are sinking (pulldown) outputs
If you wish to wire these tot a 7I96S isolated input you would
need to connect the 7I96S input common (TB3 pin 12) to +24V
and the 24V supply common to DCM.
The VFD's FOR and REV inputs must be grounded to activate
so you would connect for example:
7I96S OUT4+ --> VFD FOR
7I96S OUT4- --> DCM
Ive got the 7i96s input connected to the PSU +24v (i redid all the limits etc) but the DCM terminal of VFD is connected to the Out0- pin (for the enable function). Is it ok to have both the Out0- and the 7i96s isolated input connected to DCM on the VFD? I dont see any other way for it to get both. I actually need to do two additional inputs.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18026
- Thank you received: 5295
05 Aug 2023 02:45 #276957
by PCW
Replied by PCW on topic Logic assignments for VFD/Spindle control and EStops (7i96s)
The outputs are fully isolated from the inputs and each other
so there is no issue with any output connection (as long as their
polarity and voltage/current limitations are respected)
so there is no issue with any output connection (as long as their
polarity and voltage/current limitations are respected)
The following user(s) said Thank You: supermoto
Please Log in or Create an account to join the conversation.
- supermoto
-
Topic Author
- Offline
- Senior Member
-
Less
More
- Posts: 43
- Thank you received: 3
05 Aug 2023 14:01 - 05 Aug 2023 14:02 #277006
by supermoto
Replied by supermoto on topic Logic assignments for VFD/Spindle control and EStops (7i96s)
Excellent. Ive connected inputs from VFD, so now on to programming mesa to stop program if any signal is sent to the input.
My new question is, what assignment should be made in pncconf for that pin in order to stop everything?
Since I cant use the [ESTOP In] assignment, will the [Abort] assignment do what im seeking? See the screenshot of where it is in the wizard.
My new question is, what assignment should be made in pncconf for that pin in order to stop everything?
Since I cant use the [ESTOP In] assignment, will the [Abort] assignment do what im seeking? See the screenshot of where it is in the wizard.
Last edit: 05 Aug 2023 14:02 by supermoto.