Todd Zuercher wrote: This is to add encoder feedback to the drive so it can operate in velocity mode. The encoder can be used for both the position feedback to Linuxcnc and the velocity feedback to the drive (if you connect it to both).
Todd, Thanks for your help. I have reviewed my emails with A-M-C techs; this is a response from an earlier question.
This is the email:
"2.6.4 Encoder Velocity Mode In Encoder Velocity Mode, the input command controls the motor
velocity, with the frequency of the encoder pulses closing the velocity loop. An analog velocity
monitor output allows observation of the actual motor speed through a kHz/V scaling factor
found on the drive datasheet. The voltage value read at the velocity monitor output can
be used to determine the motor RPM through the scaling factor. See “Velocity Monitor Output” on
page 41 for the motor RPM equation.
Note
The high resolution of motor mounted encoders allows for excellent
velocity control and smooth motion at all speeds. Encoder Velocity
Mode should be used for applications requiring precise and accurate
velocity control, and is especially useful
I also read this:
2.5.2 Incremental Encoder
Analog servo drives that use encoder feedback utilize two single-ended
or differential incremental encoder inputs for velocity control. The encoder provides
incremental position feedback that can be extrapolated into very precise velocity
information. The encoder signals are read as "pulses" that the drive uses to essentially keep track of
the motor’s position and direction of rotation. Based on the speed and order in which these pulses
It seems to me I need "two single-ended" or "differential incremental
encoder" inputs for velocity control."
This is response from A-M-C:
"The AB15A100 only accepts a single ended encoder input. If you do have a differential encoder, you can just use the A+ and B+ lines and don't connect the /A and /B signals. It will still work as a single ended signal, you just won't have the benefits of a differential signal."
The manual is too large to attach. Edit: To have access to the A-M-C manuals you need password.
2nd Edit: I have approached AMC with the hope of an explanation and this is the response: If you have a differential encoder you only need to connect the A+ and B+ signals and it will work just fine.
It appears both will work. I am not shore of some of the following that is required to order encoder.
The pin out
The power supply voltage to the encoder (this is 5 VDC)
The signal output type from the encoder
The signal out voltage level from the encoder
The resolution or CPR of the encoder (2000)
many thanks!