As a general rule, use a very good power supply for the Mesa as the encoders are powered from it.
Replied by tommylight on topic Retrofitting a 3-axis VMC with DC servos - guidance needed
Shielded cable, shielding grounded on the Mesa side.From what I've measured, the issue seems to be on the encoder side.
Analog cable has 2 wires plus shielding, shield must be grounded on the Mesa side, and one of those 2 wires is the analog ground.According to the diagrams, the analog signal for the axis is connected to the machine's frame/ground.
There is no exact reference for it, see above, use a DVM to measure between analog and machine ground both in AC and DC mode > if any of those read more than a Volt or two = do not connect. If that is all correct but still does not work, you can try grounding the analog ground to machine ground through a 1K resistor for a single line, test with only a single line/analog drive/connection to mesa.Is it better to isolate the analog ground from the system ground? Under what conditions is it strictly necessary to tie both grounds together?
-
As a general rule, use a very good power supply for the Mesa as the encoders are powered from it.