Random arc signal lost
- Aciera
-
- Offline
- Administrator
-
Less
More
- Posts: 4801
- Thank you received: 2161
03 Sep 2020 18:33 - 03 Sep 2020 18:36 #180568
by Aciera
Replied by Aciera on topic Random arc signal lost
Mind you in the second schematic the resistor is between the relay contact and the (input) pin, so it actually adds the resistors value to the input impedance and thus the current is even smaller.
In the first schematic the resistor is in parallel to the input impedance and thus the combined resistance is lower, ergo the current larger.
That's how I see it anyway.
In any case, rods analysis seems entirely plausible and is a good showcase as to why relays have a minimum current rating.
In the first schematic the resistor is in parallel to the input impedance and thus the combined resistance is lower, ergo the current larger.
That's how I see it anyway.
In any case, rods analysis seems entirely plausible and is a good showcase as to why relays have a minimum current rating.
Last edit: 03 Sep 2020 18:36 by Aciera.
The following user(s) said Thank You: rodw
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12094
- Thank you received: 4132
03 Sep 2020 20:27 #180578
by rodw
Replied by rodw on topic Random arc signal lost
Its nothing to do with a debounce as software does not change the current flowing through the circuit. So back to the 7i76e and its 20k resistance for a moment. Ohms law states :
I = V/R
I = 24/20,000
I = 0.0012 Amps (or 1.2 mA), way under the 100 mA minimum current rating of the relay of my Everlast.
Granted, the 7i96 is different becasue it uses a opto isolated relay on all inputs. Maybe it does need to be in series on that board. Maybe it does not help at all. I'm no electrical engineer either.
I = V/R
I = 24/20,000
I = 0.0012 Amps (or 1.2 mA), way under the 100 mA minimum current rating of the relay of my Everlast.
Granted, the 7i96 is different becasue it uses a opto isolated relay on all inputs. Maybe it does need to be in series on that board. Maybe it does not help at all. I'm no electrical engineer either.
Please Log in or Create an account to join the conversation.
- tommylight
-
- Away
- Moderator
-
Less
More
- Posts: 21840
- Thank you received: 7456
03 Sep 2020 20:29 #180579
by tommylight
Replied by tommylight on topic Random arc signal lost
Never had the relay issue and i do use them a lot, but i tend to use quality ones so they never fail.
Please Log in or Create an account to join the conversation.
- tommylight
-
- Away
- Moderator
-
Less
More
- Posts: 21840
- Thank you received: 7456
03 Sep 2020 20:31 #180580
by tommylight
Replied by tommylight on topic Random arc signal lost
Series resistor would just worsen this issue.Granted, the 7i96 is different becasue it uses a opto isolated relay on all inputs. Maybe it does need to be in series on that board.
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12094
- Thank you received: 4132
03 Sep 2020 20:35 #180584
by rodw
I think you are right. The Everlast I had is not renowned for quality.
Replied by rodw on topic Random arc signal lost
Series resistor would just worsen this issue.Granted, the 7i96 is different becasue it uses a opto isolated relay on all inputs. Maybe it does need to be in series on that board.
I think you are right. The Everlast I had is not renowned for quality.
Please Log in or Create an account to join the conversation.
- tommylight
-
- Away
- Moderator
-
Less
More
- Posts: 21840
- Thank you received: 7456
03 Sep 2020 20:42 #180587
by tommylight
Replied by tommylight on topic Random arc signal lost
Never had anything from Everlast, so i'll take your word for it.
The following user(s) said Thank You: rodw
Please Log in or Create an account to join the conversation.
- snowgoer540
-
- Offline
- Moderator
-
Less
More
- Posts: 2561
- Thank you received: 891
03 Sep 2020 22:31 #180596
by snowgoer540
Replied by snowgoer540 on topic Random arc signal lost
It's been a busy day at work, I couldnt keep up.
Perhaps my posts were read in the wrong tone. I wasn't trying to say anyone was wrong, I was trying to understand, which while I understand why the resistor must be in parallel with the pull up resistor, and lower resistance ccauses the circuit to pull more amperage, I don't understand exactly where the resistor is in the system and how it interfaces with whats in the MESA card to do that...
At any rate, yes, I'm aware that software doesn't debounce current. However, there is a lot of hysteresis when a relay makes contact, just like a button or a switch, which I'm sure could be seen with halscope if I ever bother to learn it
What debounce does do is ignore that hysteresis until it settles down, so LinuxCNC can be SURE whether or not the input is ON or OFF. A switch "bounce" plot example of what needs to be ignored with debounce:
What Phill and I thought was going on (at least with Cody and My Hypertherms, but this will affect all dry contact arc-ok's) is that because there is no debounce on the arc-ok signal by default, but it's a dry contact relay. LinuxCNC is fast enough to read the hysteresis in the switching and as such sees it go from ON to OFF and thinks of this as losing the arc-ok (because technically it did, even though the torch didn't really flame out). For Cody, his table was unusable, he would routinely experience super short torch fires, with a valid arc lost error.
But alas, it's fixed! The hal connections file I made him for his table this morning, which now includes a debounce on the arc-ok input solved his problem. His table works 100% perfect now. And his wasn't intermittent, it just plain didn't work. I mean think about it, it's a switch, we debounce every other form of physical switching, Arc-OK should be debounced by default too.
@Rod, I suspect that your resistor method works because it reduces the hysteresis involved with the Arc-OK going true. Perhaps the .1A of current causes a spark and temporarily "welds" the contacts together... something that probably doesn't happen with 5mA of current (I'd love to see some halscope plots of your method vs a power source that doesnt have a resistor). At any rate, I hesitate to both recommend a resistor that gets hot as a solution, and add it to my table because in addition to the extra heat I'm not sure it's the same for every MESA card, and frankly, I don't fully understand why it works. Debouncing the input, I understand, and it works.
Perhaps my posts were read in the wrong tone. I wasn't trying to say anyone was wrong, I was trying to understand, which while I understand why the resistor must be in parallel with the pull up resistor, and lower resistance ccauses the circuit to pull more amperage, I don't understand exactly where the resistor is in the system and how it interfaces with whats in the MESA card to do that...
At any rate, yes, I'm aware that software doesn't debounce current. However, there is a lot of hysteresis when a relay makes contact, just like a button or a switch, which I'm sure could be seen with halscope if I ever bother to learn it
What Phill and I thought was going on (at least with Cody and My Hypertherms, but this will affect all dry contact arc-ok's) is that because there is no debounce on the arc-ok signal by default, but it's a dry contact relay. LinuxCNC is fast enough to read the hysteresis in the switching and as such sees it go from ON to OFF and thinks of this as losing the arc-ok (because technically it did, even though the torch didn't really flame out). For Cody, his table was unusable, he would routinely experience super short torch fires, with a valid arc lost error.
But alas, it's fixed! The hal connections file I made him for his table this morning, which now includes a debounce on the arc-ok input solved his problem. His table works 100% perfect now. And his wasn't intermittent, it just plain didn't work. I mean think about it, it's a switch, we debounce every other form of physical switching, Arc-OK should be debounced by default too.
@Rod, I suspect that your resistor method works because it reduces the hysteresis involved with the Arc-OK going true. Perhaps the .1A of current causes a spark and temporarily "welds" the contacts together... something that probably doesn't happen with 5mA of current (I'd love to see some halscope plots of your method vs a power source that doesnt have a resistor). At any rate, I hesitate to both recommend a resistor that gets hot as a solution, and add it to my table because in addition to the extra heat I'm not sure it's the same for every MESA card, and frankly, I don't fully understand why it works. Debouncing the input, I understand, and it works.
Attachments:
Please Log in or Create an account to join the conversation.
- phillc54
-
- Offline
- Platinum Member
-
Less
More
- Posts: 5711
- Thank you received: 2100
03 Sep 2020 23:05 #180599
by phillc54
Replied by phillc54 on topic Random arc signal lost
Glad you got it going, it will be interesting to see if it performs reliably. Did you need to change the debounce value at all.
I think there are two different issues being discussed here, one is using the debounce component to nullify contact bounce and the other is the minimum current required to flow through the relay contacts.
I think there are two different issues being discussed here, one is using the debounce component to nullify contact bounce and the other is the minimum current required to flow through the relay contacts.
Please Log in or Create an account to join the conversation.
- snowgoer540
-
- Offline
- Moderator
-
Less
More
- Posts: 2561
- Thank you received: 891
03 Sep 2020 23:30 #180600
by snowgoer540
No, no need on this end to change the period from 5. I told him if it comes back at all, to let me know. I do plan to try to grab some halscope plots of my table.
I agree, we are talking too different issues for sure.
For the minimum current through a relay, my albeit short, research said that it's a number manufactures use based around reliability limits and making sure there are guidelines to establish mean time to failure. In our use case, I'm not sure it matters a whole lot, if it did, I would think it would be mentioned in the power source manuals. But admittedly I'd be willing to be proven wrong.
Replied by snowgoer540 on topic Random arc signal lost
Glad you got it going, it will be interesting to see if it performs reliably. Did you need to change the debounce value at all.
I think there are two different issues being discussed here, one is using the debounce component to nullify contact bounce and the other is the minimum current required to flow through the relay contacts.
No, no need on this end to change the period from 5. I told him if it comes back at all, to let me know. I do plan to try to grab some halscope plots of my table.
I agree, we are talking too different issues for sure.
For the minimum current through a relay, my albeit short, research said that it's a number manufactures use based around reliability limits and making sure there are guidelines to establish mean time to failure. In our use case, I'm not sure it matters a whole lot, if it did, I would think it would be mentioned in the power source manuals. But admittedly I'd be willing to be proven wrong.
Please Log in or Create an account to join the conversation.
- phillc54
-
- Offline
- Platinum Member
-
Less
More
- Posts: 5711
- Thank you received: 2100
03 Sep 2020 23:37 #180601
by phillc54
It would be nice to see a before and after from Cody's table.
Replied by phillc54 on topic Random arc signal lost
No, no need on this end to change the period from 5. I told him if it comes back at all, to let me know. I do plan to try to grab some halscope plots of my table..
It would be nice to see a before and after from Cody's table.
Please Log in or Create an account to join the conversation.