I have read this at post #9 at this link: www.cnczone.com/forums/servo-motors-driv...a20-torque-mode.html
This describes that AMC drivers require a way to inhibit the drive. Does this apply to my application?
Many thanks, for all help is warmly welcomed.
"Re: Setting up AMC BE25A20 in torque mode?
I am currently working on a retrofit using the Mesa 7i92, 7i77, and AMC 30A8 drives in torque mode which should be very similar to your setup. I don't know if you have seen them, but AMC has multiple manuals on their site that provide details on how to setup the drives in torque mode, adjust offsets, and such. Go to their website and search for your model:
www.a-m-c.com/products/?page=product&id=25A20
This will give you the datasheet for your specific model. On the above page, if you click on the reserved and discontinued items link, there will be a link to the classic analog drives HW manual which has a bunch of good information on setting up the drives. A direct link is here:
www.a-m-c.com/wp-content/upl...alog_Panel.pdf
PCW_MESA is correct in that the inhibit line left open enables the drive by default (it has an internal pull-up to +5VDC). I wanted the drive to be disabled by default and and didn't want to modify the drive's circuit board so I am using a normally closed solid state relay to pull the inhibit line to ground at power up or any other time when either the E-Stop is triggered or the drive enable switch isn't turned on. I also use another NC SSR for the fault line feedback to the 7i77 since I'm using 24VDC for field IO and the AMC drive uses a 5VDC TTL output. I can provide a hand drawn schematic for my interface board if you are interested. It uses 6 x CPC1333G ICs (4 pin DIP NC SPST SSR) and 6 resistors for current limiting."
This describes that AMC drivers require a way to inhibit the drive. Does this apply to my application?
Many thanks, for all help is warmly welcomed.
"Re: Setting up AMC BE25A20 in torque mode?
I am currently working on a retrofit using the Mesa 7i92, 7i77, and AMC 30A8 drives in torque mode which should be very similar to your setup. I don't know if you have seen them, but AMC has multiple manuals on their site that provide details on how to setup the drives in torque mode, adjust offsets, and such. Go to their website and search for your model:
www.a-m-c.com/products/?page=product&id=25A20
This will give you the datasheet for your specific model. On the above page, if you click on the reserved and discontinued items link, there will be a link to the classic analog drives HW manual which has a bunch of good information on setting up the drives. A direct link is here:
www.a-m-c.com/wp-content/upl...alog_Panel.pdf
PCW_MESA is correct in that the inhibit line left open enables the drive by default (it has an internal pull-up to +5VDC). I wanted the drive to be disabled by default and and didn't want to modify the drive's circuit board so I am using a normally closed solid state relay to pull the inhibit line to ground at power up or any other time when either the E-Stop is triggered or the drive enable switch isn't turned on. I also use another NC SSR for the fault line feedback to the 7i77 since I'm using 24VDC for field IO and the AMC drive uses a 5VDC TTL output. I can provide a hand drawn schematic for my interface board if you are interested. It uses 6 x CPC1333G ICs (4 pin DIP NC SPST SSR) and 6 resistors for current limiting."
Please Log in or Create an account to join the conversation.
- new2linux
- Offline
- Platinum Member
-
Less
More
- Posts: 711
- Thank you received: 9
28 Apr 2022 13:22 #241479
by new2linux
Replied by new2linux on topic Set up using AMC AB15A100 drives, brushed DC motor Prototrak Plus with Encoders
Many thanks andypugh for your help! This is you offering the diagram describing "DC servos with tachometers. A +/- 10V analogue control signal into the drive" (12 Dec 2016 09:55 #83938 the link:
forum.linuxcnc.org/12-milling/31949-deck...4ma-retrofit?start=0)
Could I start with this diagram and where the tachometers attach, replace with encoder input??
The diagram is at this link, I will try to attach pic: forum.linuxcnc.org/media/kunena/attachments/723/Deckel_p115.pdf
forum.linuxcnc.org/12-milling/31949-deck...4ma-retrofit?start=0)
Could I start with this diagram and where the tachometers attach, replace with encoder input??
The diagram is at this link, I will try to attach pic: forum.linuxcnc.org/media/kunena/attachments/723/Deckel_p115.pdf
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 19898
- Thank you received: 4655
28 Apr 2022 22:09 #241576
by andypugh
Old analogue drives with tachometers used a very simple scheme where the control voltage and the tachometer voltage were compared and the motor voltage set accordingly. Encoders don't output a voltage proportional to speed, so more interfacing is needed.
Now, if the drives are already conffigured to close an internal velocity loop from the encoder pulses, then what you describe will work.
But, is it?
Replied by andypugh on topic Set up using AMC AB15A100 drives, brushed DC motor Prototrak Plus with Encoders
Probably not.Could I start with this diagram and where the tachometers attach, replace with encoder input??
Old analogue drives with tachometers used a very simple scheme where the control voltage and the tachometer voltage were compared and the motor voltage set accordingly. Encoders don't output a voltage proportional to speed, so more interfacing is needed.
Now, if the drives are already conffigured to close an internal velocity loop from the encoder pulses, then what you describe will work.
But, is it?
The following user(s) said Thank You: new2linux
Please Log in or Create an account to join the conversation.
- new2linux
- Offline
- Platinum Member
-
Less
More
- Posts: 711
- Thank you received: 9
29 Apr 2022 16:38 #241649
by new2linux
Replied by new2linux on topic Set up using AMC AB15A100 drives, brushed DC motor Prototrak Plus with Encoders
andypugh, Many, many thanks!! I have read this response several times,
"are already configured to close an internal velocity loop from the encoder pulses,"
I can/will research this more if necessary, if this will lead to success.
Or if there is a way to use the P1 Connector; location: Pin 8 Current Monitor (Note in AMC AB15A100 Drive manual, says: analogue output signal proportional to actual current output). Is this a potential workaround or part of a successful approach?
Many thanks!! All help is warmly welcomed.
"are already configured to close an internal velocity loop from the encoder pulses,"
I can/will research this more if necessary, if this will lead to success.
Or if there is a way to use the P1 Connector; location: Pin 8 Current Monitor (Note in AMC AB15A100 Drive manual, says: analogue output signal proportional to actual current output). Is this a potential workaround or part of a successful approach?
Many thanks!! All help is warmly welcomed.
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 19898
- Thank you received: 4655
01 May 2022 23:07 #241818
by andypugh
Replied by andypugh on topic Set up using AMC AB15A100 drives, brushed DC motor Prototrak Plus with Encoders
If the drives only mention that current is proportional to input voltage then they are torque-mode drives, and the encoders go straight to LinuxCNC, not to the drives.
This is fairly common, both my servo machines work that way.
This is fairly common, both my servo machines work that way.
The following user(s) said Thank You: new2linux
Please Log in or Create an account to join the conversation.
- new2linux
- Offline
- Platinum Member
-
Less
More
- Posts: 711
- Thank you received: 9
04 May 2022 19:10 - 13 Jun 2022 18:23 #241996
by new2linux
Replied by new2linux on topic Set up using AMC AB15A100 drives, brushed DC motor Prototrak Plus with Encoders
Many, many thanks, andypugh, I have read your reply:I have just got off phone with news: I am working with AMC support engineer a question has come up about when booting up LinuxCnc it appears as if I had forgotten to power up the power supply for the AMC drives
Edit: the proper wiring diagram, dated 6/2022 attached.
Edit: the proper wiring diagram, dated 6/2022 attached.
Last edit: 13 Jun 2022 18:23 by new2linux. Reason: new info; attach diagram; add equation for POT2 Edit: Proper wiring diagram attached dated 6/2022
Please Log in or Create an account to join the conversation.
- new2linux
- Offline
- Platinum Member
-
Less
More
- Posts: 711
- Thank you received: 9
06 May 2022 16:18 #242152
by new2linux
Replied by new2linux on topic Set up using AMC AB15A100 drives, brushed DC motor Prototrak Plus with Encoders
Attachments:
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 19898
- Thank you received: 4655
06 May 2022 19:35 #242167
by andypugh
Replied by andypugh on topic Set up using AMC AB15A100 drives, brushed DC motor Prototrak Plus with Encoders
5i25.0.7i77.0.1.analogoutout0-scalemax not found
This might indicate that the 7i77 field power supply (which runs a small processor on the 7i77 ) might not be connected.
This is (typically) the 24V supply used for limit switches etc, which it is quite reasonable to not expect to need yet. (It doesn't have to be 24V, anywhere from 5 to 30 is OK)
This might indicate that the 7i77 field power supply (which runs a small processor on the 7i77 ) might not be connected.
This is (typically) the 24V supply used for limit switches etc, which it is quite reasonable to not expect to need yet. (It doesn't have to be 24V, anywhere from 5 to 30 is OK)
The following user(s) said Thank You: new2linux
Please Log in or Create an account to join the conversation.
- new2linux
- Offline
- Platinum Member
-
Less
More
- Posts: 711
- Thank you received: 9
06 May 2022 19:59 - 06 May 2022 20:43 #242170
by new2linux
Replied by new2linux on topic Set up using AMC AB15A100 drives, brushed DC motor Prototrak Plus with Encoders
Many thanks, andypugh!!
I will be checking the 2 small transformers for voltage over the weekend.
Many thanks for your time.
Edit: There are 2 transformers, 1 is 5.6 v DC; the other 1 is burnt out, it was 24 v DC, went to TB-2. I plan to try the other 5.6 v DC transformer to both TB-1 & TB-2.
Many thanks, I am very greatful for the help!!
I will be checking the 2 small transformers for voltage over the weekend.
Many thanks for your time.
Edit: There are 2 transformers, 1 is 5.6 v DC; the other 1 is burnt out, it was 24 v DC, went to TB-2. I plan to try the other 5.6 v DC transformer to both TB-1 & TB-2.
Many thanks, I am very greatful for the help!!
Last edit: 06 May 2022 20:43 by new2linux. Reason: note about transformers
Please Log in or Create an account to join the conversation.
- new2linux
- Offline
- Platinum Member
-
Less
More
- Posts: 711
- Thank you received: 9
08 May 2022 14:14 #242302
by new2linux
Replied by new2linux on topic Set up using AMC AB15A100 drives, brushed DC motor Prototrak Plus with Encoders
Over the weekend, I used the 5.6 v DC transformer (power supply to TB-1) & then, used a 12 v rechargeable battery to supply power to TB-2. The same error message appears both times, "5i25.0.7i77.0.1.analogoutout0-scalemax not found". To be clear, TB-5, pins 1 & 2 are not connected to anything, yet. I have ordered replacement 24v DC transformer.
Many, many thanks for helping, all suggestions are warmly welcomed.
Many, many thanks for helping, all suggestions are warmly welcomed.
Please Log in or Create an account to join the conversation.
Moderators: piasdom
- Hardware & Machines
- CNC Machines
- Milling Machines
- Set up using AMC AB15A100 drives, brushed DC motor Prototrak Plus with Encoders
Time to create page: 0.672 seconds