Thanks for the offer Rod but I have a spare THCAD10 on my desk that Ill put in to test the issue.
Replied by thefabricator03 on topic THCAD Environmental Fluctuations
Would you like me to lend you a THCAD so you can test by swapping out?
Send me an email and I can express it down tomorrow with TNT.
Thanks for the offer Rod but I have a spare THCAD10 on my desk that Ill put in to test the issue.
Please Log in or Create an account to join the conversation.
- thefabricator03
-
Topic Author
- Visitor
-
27 Jan 2021 19:48 #196803
by thefabricator03
For some reason when I first built my controller I mounted my THCAD in a small steel box outside of the control box, looking back it was a silly thing to do so that is why I have used a external 24VDC to 5VDC step down transformer.
Replied by thefabricator03 on topic THCAD Environmental Fluctuations
I'm not understanding your circuit. From memory your THCAD is in your control panel so you should be able to power the THCAD from one of the 5 volt signals on the 7i76e provided for that purpose.
For some reason when I first built my controller I mounted my THCAD in a small steel box outside of the control box, looking back it was a silly thing to do so that is why I have used a external 24VDC to 5VDC step down transformer.
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12156
- Thank you received: 4149
27 Jan 2021 21:18 #196818
by rodw
How far away? There should not be much voltage loss.
I think you should duck down to Jaycar and grab some shielded cable and power the THCAD as PCW said. If you use 4 core cable, use 2 wires for each side. That certainly eliminates the power supply as being the culprit.
If it happens again, measure the voltage on the THCAD input terminals coming from the plasma cutter. When I was chasing stuff down like this, once I grabbed some old multimeter leads, cut the ends off and permanently wired them in.
Replied by rodw on topic THCAD Environmental Fluctuations
I'm not understanding your circuit. From memory your THCAD is in your control panel so you should be able to power the THCAD from one of the 5 volt signals on the 7i76e provided for that purpose.
For some reason when I first built my controller I mounted my THCAD in a small steel box outside of the control box, looking back it was a silly thing to do so that is why I have used a external 24VDC to 5VDC step down transformer.
How far away? There should not be much voltage loss.
I think you should duck down to Jaycar and grab some shielded cable and power the THCAD as PCW said. If you use 4 core cable, use 2 wires for each side. That certainly eliminates the power supply as being the culprit.
If it happens again, measure the voltage on the THCAD input terminals coming from the plasma cutter. When I was chasing stuff down like this, once I grabbed some old multimeter leads, cut the ends off and permanently wired them in.
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12156
- Thank you received: 4149
27 Jan 2021 21:20 #196820
by rodw
Replied by rodw on topic THCAD Environmental Fluctuations
Actually, are the THCAD outputs shielded? If not, redo with shielded cable. In that case, just run the one shielded cable for both power and frequency signals
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21980
- Thank you received: 7480
27 Jan 2021 21:25 #196821
by tommylight
Replied by tommylight on topic THCAD Environmental Fluctuations
I use those small converters on all my recent machines, a few days back one of them went to 5.3V for no particular reason, further investigation and the subsequent change might come ... as soon as the temperature goes a bit north, -6 now.
BTW 7i92 and THCAD are OK.
BTW 7i92 and THCAD are OK.
The following user(s) said Thank You: rodw, thefabricator03
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12156
- Thank you received: 4149
27 Jan 2021 21:27 #196822
by rodw
In fact, some CAT6 network cable would do. Use one twisted pair for +5v joined together, another pair for -5v but bring the frequency back on a single twisted pair for best noise immunity. See the mesa manual for the 7i76/7i73 connection if in doubt as Mesa powers the 7i73 the same way.
Replied by rodw on topic THCAD Environmental Fluctuations
Actually, are the THCAD outputs shielded? If not, redo with shielded cable. In that case, just run the one shielded cable for both power and frequency signals
In fact, some CAT6 network cable would do. Use one twisted pair for +5v joined together, another pair for -5v but bring the frequency back on a single twisted pair for best noise immunity. See the mesa manual for the 7i76/7i73 connection if in doubt as Mesa powers the 7i73 the same way.
The following user(s) said Thank You: thefabricator03
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12156
- Thank you received: 4149
02 Feb 2021 12:55 - 02 Feb 2021 12:57 #197414
by rodw
Replied by rodw on topic THCAD Environmental Fluctuations
Well, I think I know whats going on.
I set up a 7i76e on my desk at home and decided to play with a THCAD-5 and a 24 Volt power supply I installed for Ohmic sensing.
I had not set up any scaling and was just observing encoder velocity
I was getting all sorts of crazy fluctuations. They went away if I disconnected both THCAD inputs.
As soon as I connected either +ve or -ve, the fluctuations returned.
So I plotted them in halscope
There is a perfect 50 Hz AC ripple!
So then I disconnected the THCAD from ground (being to a DIN rail via a clamp) and the signal was rock solid.
The mains was also grounded to the din rail
So I think that your problem is a ground loop emanating from somewhere in your building on hot days due to some random dodginess somewhere.
I think the solution might lay in what has been suggested earlier,
1. Remove the external power supply
2. Power from the 7i76e
3. Install a quality RFI filter on the power input (Jaycar may not qualify here!)
Eventually I'll try and add a mains RFI filter and observe the response.
I set up a 7i76e on my desk at home and decided to play with a THCAD-5 and a 24 Volt power supply I installed for Ohmic sensing.
I had not set up any scaling and was just observing encoder velocity
I was getting all sorts of crazy fluctuations. They went away if I disconnected both THCAD inputs.
As soon as I connected either +ve or -ve, the fluctuations returned.
So I plotted them in halscope
There is a perfect 50 Hz AC ripple!
So then I disconnected the THCAD from ground (being to a DIN rail via a clamp) and the signal was rock solid.
The mains was also grounded to the din rail
So I think that your problem is a ground loop emanating from somewhere in your building on hot days due to some random dodginess somewhere.
I think the solution might lay in what has been suggested earlier,
1. Remove the external power supply
2. Power from the 7i76e
3. Install a quality RFI filter on the power input (Jaycar may not qualify here!)
Eventually I'll try and add a mains RFI filter and observe the response.
Last edit: 02 Feb 2021 12:57 by rodw.
The following user(s) said Thank You: thefabricator03
Please Log in or Create an account to join the conversation.
- thefabricator03
-
Topic Author
- Visitor
-
02 Feb 2021 13:01 #197415
by thefabricator03
Replied by thefabricator03 on topic THCAD Environmental Fluctuations
Thanks for that Rod, I think your on the money. My first thought was the edges of the plates I was cutting then this first occurred is that they looked like a sine wave. They were perfectly cut in a wave pattern. I had a power cable near the THCAD box and I thought that it might be causing some interference somehow.
I will implement those suggestions and report back.Its been cooler here the last couple of days and I have not had the issue reoccur.
I will implement those suggestions and report back.Its been cooler here the last couple of days and I have not had the issue reoccur.
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12156
- Thank you received: 4149
02 Feb 2021 13:08 #197416
by rodw
Replied by rodw on topic THCAD Environmental Fluctuations
The following user(s) said Thank You: dvn4life1972
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21980
- Thank you received: 7480
02 Feb 2021 13:17 #197418
by tommylight
Replied by tommylight on topic THCAD Environmental Fluctuations
That brings up the earthing/grounding topic i had to deal with at a clients site, twice till i figured out what the hell was going on.
During summer the earth gets dry and since the grounding IS in that ground the conductivity becomes "not good".
Solved it by moving the grounding to a water tap/pipe, plenty of metal going through ground and mostly moist !
During summer the earth gets dry and since the grounding IS in that ground the conductivity becomes "not good".
Solved it by moving the grounding to a water tap/pipe, plenty of metal going through ground and mostly moist !
The following user(s) said Thank You: thefabricator03