- Beckhoff ethercat 64 with bit linuxcnc, How to install.
Beckhoff ethercat 64 with bit linuxcnc, How to install.
- Sviper
- Offline
- Senior Member
Less
More
- Posts: 76
- Thank you received: 9
23 Nov 2022 18:16 - 23 Nov 2022 18:16 #257497
by Sviper
Replied by Sviper on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
my ethercat test maschine
Last edit: 23 Nov 2022 18:16 by Sviper.
Please Log in or Create an account to join the conversation.
- boyzo
- Offline
- Senior Member
Less
More
- Posts: 76
- Thank you received: 3
23 Nov 2022 22:29 #257523
by boyzo
<masters>
<master idx="0" appTimePeriod="1000000" refClockSyncCycles="1">
<slave idx="0" type="EK1100" name="EK1100"/>
<slave idx="1" type="EL1809" name="EL1809"/>
<slave idx="2" type="EL2809" name="EL2809"/>
<slave idx="3" type="generic" vid="00000002" pid="14536012" configPdos="true">
<syncManager idx="0" dir="out"> </syncManager>
<syncManager idx="1" dir="in"> </syncManager>
<syncManager idx="2" dir="out">
<pdo idx="1600">
<pdoEntry idx="7000" subIdx="03" bitLen="64" halType="complex">
<complexEntry bitLen="1" halPin="X-cmd-SwitchOn" halType="bit"/>
<complexEntry bitLen="1" halPin="X-cmd-EnableVoltage" halType="bit"/>
<complexEntry bitLen="1" halPin="X-cmd-/QuickStop" halType="bit"/>
based on pdos output:
=== Master 0, Slave 3 ===
SM0: PhysAddr 0x1800, DefaultSize 128, ControlRegister 0x26, Enable 1
SM1: PhysAddr 0x1a00, DefaultSize 128, ControlRegister 0x22, Enable 1
SM2: PhysAddr 0x1000, DefaultSize 0, ControlRegister 0x24, Enable 1
RxPDO 0x0018 "MDT 1"
PDO entry 0x0086:00, 16 bit, "Master control word"
PDO entry 0x002f:00, 32 bit, "Position command value"
RxPDO 0x1018 "MDT 2"
PDO entry 0x0086:00, 16 bit, "Master control word"
PDO entry 0x002f:00, 32 bit, "Position command value"
SM3: PhysAddr 0x1100, DefaultSize 0, ControlRegister 0x22, Enable 1
TxPDO 0x0010 "AT 1"
PDO entry 0x0087:00, 16 bit, "Drive status word"
PDO entry 0x0033:00, 32 bit, "Position feedback 1 value"
PDO entry 0x00bd:00, 32 bit, "Following distance"
TxPDO 0x1010 "AT 2"
PDO entry 0x0087:00, 16 bit, "Drive status word"
PDO entry 0x0033:00, 32 bit, "Position feedback 1 value"
PDO entry 0x00bd:00, 32 bit, "Following distance"
I know it is not correct, but I don't find documentation on relationship between pdos output and definition.
Is there any good documentation I can use?
Replied by boyzo on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
This is how I changed your .xml file:my ethercat test maschine
<masters>
<master idx="0" appTimePeriod="1000000" refClockSyncCycles="1">
<slave idx="0" type="EK1100" name="EK1100"/>
<slave idx="1" type="EL1809" name="EL1809"/>
<slave idx="2" type="EL2809" name="EL2809"/>
<slave idx="3" type="generic" vid="00000002" pid="14536012" configPdos="true">
<syncManager idx="0" dir="out"> </syncManager>
<syncManager idx="1" dir="in"> </syncManager>
<syncManager idx="2" dir="out">
<pdo idx="1600">
<pdoEntry idx="7000" subIdx="03" bitLen="64" halType="complex">
<complexEntry bitLen="1" halPin="X-cmd-SwitchOn" halType="bit"/>
<complexEntry bitLen="1" halPin="X-cmd-EnableVoltage" halType="bit"/>
<complexEntry bitLen="1" halPin="X-cmd-/QuickStop" halType="bit"/>
based on pdos output:
=== Master 0, Slave 3 ===
SM0: PhysAddr 0x1800, DefaultSize 128, ControlRegister 0x26, Enable 1
SM1: PhysAddr 0x1a00, DefaultSize 128, ControlRegister 0x22, Enable 1
SM2: PhysAddr 0x1000, DefaultSize 0, ControlRegister 0x24, Enable 1
RxPDO 0x0018 "MDT 1"
PDO entry 0x0086:00, 16 bit, "Master control word"
PDO entry 0x002f:00, 32 bit, "Position command value"
RxPDO 0x1018 "MDT 2"
PDO entry 0x0086:00, 16 bit, "Master control word"
PDO entry 0x002f:00, 32 bit, "Position command value"
SM3: PhysAddr 0x1100, DefaultSize 0, ControlRegister 0x22, Enable 1
TxPDO 0x0010 "AT 1"
PDO entry 0x0087:00, 16 bit, "Drive status word"
PDO entry 0x0033:00, 32 bit, "Position feedback 1 value"
PDO entry 0x00bd:00, 32 bit, "Following distance"
TxPDO 0x1010 "AT 2"
PDO entry 0x0087:00, 16 bit, "Drive status word"
PDO entry 0x0033:00, 32 bit, "Position feedback 1 value"
PDO entry 0x00bd:00, 32 bit, "Following distance"
I know it is not correct, but I don't find documentation on relationship between pdos output and definition.
Is there any good documentation I can use?
Please Log in or Create an account to join the conversation.
- db1981
- Offline
- Platinum Member
Less
More
- Posts: 790
- Thank you received: 275
24 Nov 2022 09:47 - 24 Nov 2022 09:48 #257551
by db1981
Replied by db1981 on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
i have very less time at the moment.....
getting an ax5xxx running with the generic driver will get an very heavy task.
This is an SOE (Sercos) Drive, the drives stores no config data inside.
You have to complete config the drive with initcmds.( drive setup, motor data, pdo config etc.) every time you start lcnc.
the easiest way is to create an working drive config with Twincat, and then export the config data to get an initcmds.xml for the drive setup.
there are native drivers in lcnc-ethercat for the AX5xxx, for velocity control mode.
There are many threads with AX5XXX around here, where i have explained everything in detail....
there are also examples in linuxcnc-ethercat github.
getting an ax5xxx running with the generic driver will get an very heavy task.
This is an SOE (Sercos) Drive, the drives stores no config data inside.
You have to complete config the drive with initcmds.( drive setup, motor data, pdo config etc.) every time you start lcnc.
the easiest way is to create an working drive config with Twincat, and then export the config data to get an initcmds.xml for the drive setup.
there are native drivers in lcnc-ethercat for the AX5xxx, for velocity control mode.
There are many threads with AX5XXX around here, where i have explained everything in detail....
there are also examples in linuxcnc-ethercat github.
Last edit: 24 Nov 2022 09:48 by db1981.
The following user(s) said Thank You: rodw
Please Log in or Create an account to join the conversation.
- boyzo
- Offline
- Senior Member
Less
More
- Posts: 76
- Thank you received: 3
28 Nov 2022 22:23 #257901
by boyzo
Can you please explain, what this statements represent and where I can get values from?
Replied by boyzo on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
I did export config from TC2 and edit .xml . I use linuxcnc-ethercat / examples / initcmds /AX5206-AM8032-async.xml as example. Then I create ethercat.xml, but I do not understand several tags and values there.the easiest way is to create an working drive config with Twincat, and then export the config data to get an initcmds.xml for the drive setup.
there are native drivers in lcnc-ethercat for the AX5xxx, for velocity control mode.
There are many threads with AX5XXX around here, where i have explained everything in detail....
there are also examples in linuxcnc-ethercat github.
Can you please explain, what this statements represent and where I can get values from?
Please Log in or Create an account to join the conversation.
- db1981
- Offline
- Platinum Member
Less
More
- Posts: 790
- Thank you received: 275
28 Nov 2022 22:57 #257912
by db1981
Replied by db1981 on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
oh, the example is very old...
We have done an native AX Driver in the meantime.
this is all needed for AX Drive.
the dcConf line tells the master the DC Parameters for the Slave (get it from AX manual or device description xml)
the other lines from the example are for setting up an AX with the generic driver
We have done an native AX Driver in the meantime.
<slave idx="3" type="AX5206" >
<initCmds filename="AX5206-AM8032-async.xml"/>
<!--
IMPORTANT: in this case (sync1Cycle = n * sync0Cycle) sync1Cycle must be appTimePeriod - sync0Cycle)
-->
<dcConf assignActivate="730" sync0Cycle="250000" sync0Shift="50000" sync1Cycle="750000" sync1Shift="250000"/>
</slave>
this is all needed for AX Drive.
the dcConf line tells the master the DC Parameters for the Slave (get it from AX manual or device description xml)
the other lines from the example are for setting up an AX with the generic driver
Please Log in or Create an account to join the conversation.
- rodw
- Away
- Platinum Member
Less
More
- Posts: 10711
- Thank you received: 3533
28 Nov 2022 23:39 #257918
by rodw
Replied by rodw on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
Very interesting. What motors would you pair with a AX2506?oh, the example is very old...
We have done an native AX Driver in the meantime.
this is all needed for AX Drive.
Please Log in or Create an account to join the conversation.
- boyzo
- Offline
- Senior Member
Less
More
- Posts: 76
- Thank you received: 3
29 Nov 2022 13:42 #257975
by boyzo
Should I include my generated without any changes or I need to modify something?
Replied by boyzo on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
Super, thank you.oh, the example is very old...
We have done an native AX Driver in the meantime.
<slave idx="3" type="AX5206" > <initCmds filename="AX5206-AM8032-async.xml"/> <!-- IMPORTANT: in this case (sync1Cycle = n * sync0Cycle) sync1Cycle must be appTimePeriod - sync0Cycle) --> <dcConf assignActivate="730" sync0Cycle="250000" sync0Shift="50000" sync1Cycle="750000" sync1Shift="250000"/> </slave> this is all needed for AX Drive.
Should I include my generated
AX5206-AM8032-async.xml
Please Log in or Create an account to join the conversation.
- boyzo
- Offline
- Senior Member
Less
More
- Posts: 76
- Thank you received: 3
29 Nov 2022 13:46 #257977
by boyzo
Replied by boyzo on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
I will use Beckhoff AM8541-1D10 2,37 Nm
Very interesting. What motors would you pair with a AX2506?
The following user(s) said Thank You: rodw
Please Log in or Create an account to join the conversation.
- db1981
- Offline
- Platinum Member
Less
More
- Posts: 790
- Thank you received: 275
29 Nov 2022 14:05 #257980
by db1981
Replied by db1981 on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
you have to use our AX5203.xml . Initcmds looks ok.
Seems that there is one </initcmds> to much at the end of the file.
Seems that there is one </initcmds> to much at the end of the file.
Please Log in or Create an account to join the conversation.
- boyzo
- Offline
- Senior Member
Less
More
- Posts: 76
- Thank you received: 3
29 Nov 2022 23:10 #258044
by boyzo
More I dive deep into, more questions I have.
How do I define hal I/O bits and other values I want to use, as example from AX5203.xml I want to use position feedback value 1
<Object>
<Index>51</Index>
<!-- S-0-0051 -->
<Name LcId="1033"><![CDATA[Position feedback value 1 (motor feedback)]]></Name>
<Comment LcId="1033"><![CDATA[The position feedback value 1 (motor feedback) displays the actual position of the motor feedback.]]></Comment>
<Type>DINT</Type>
<BitSize>32</BitSize>
<Flags>
<PdoMapping>T</PdoMapping>
<Attribute>#x70220001</Attribute>
</Flags>
<Properties>
<Property>
<Name>UnitName</Name>
<Desc LcId="1033"><![CDATA[inc]]></Desc>
</Property>
<Property>
<Name>PROP_GROUP</Name>
<Value>6</Value>
</Property>
<Property>
<Name>PossibleListMemberOf</Name>
<Value>903</Value>
</Property>
</Properties>
</Object>
How do I use some other functions like DriveEnable? How do I find and define correct bit in my xml file?
Is internal communication between lcnc and drive done through ethercat telegram?
As I see, you put enormous amount of work in lclc ethercat project, but what I can not find is some documentation that I can use and find most of this answers by myself, not bother you every day.
Many thanks
Replied by boyzo on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
I downloaded AX configuration from sittner/ethercat/etc/xml/Beckhoff AX5xxx/Beckhoff AX5203-xxxx-0203 Dict.xml.you have to use our AX5203.xml . Initcmds looks ok.
Seems that there is one </initcmds> to much at the end of the file.
More I dive deep into, more questions I have.
How do I define hal I/O bits and other values I want to use, as example from AX5203.xml I want to use position feedback value 1
<Object>
<Index>51</Index>
<!-- S-0-0051 -->
<Name LcId="1033"><![CDATA[Position feedback value 1 (motor feedback)]]></Name>
<Comment LcId="1033"><![CDATA[The position feedback value 1 (motor feedback) displays the actual position of the motor feedback.]]></Comment>
<Type>DINT</Type>
<BitSize>32</BitSize>
<Flags>
<PdoMapping>T</PdoMapping>
<Attribute>#x70220001</Attribute>
</Flags>
<Properties>
<Property>
<Name>UnitName</Name>
<Desc LcId="1033"><![CDATA[inc]]></Desc>
</Property>
<Property>
<Name>PROP_GROUP</Name>
<Value>6</Value>
</Property>
<Property>
<Name>PossibleListMemberOf</Name>
<Value>903</Value>
</Property>
</Properties>
</Object>
How do I use some other functions like DriveEnable? How do I find and define correct bit in my xml file?
Is internal communication between lcnc and drive done through ethercat telegram?
As I see, you put enormous amount of work in lclc ethercat project, but what I can not find is some documentation that I can use and find most of this answers by myself, not bother you every day.
Many thanks
Please Log in or Create an account to join the conversation.